radiohead
Thanks radiohead is there any scenarios then you would be comfortable doing what I proposed....2 double sockets off 4mm from ring.
Absolutely not. Bs 7671 permits a maximum of 1 double outlet to be on an unfused spur from a ring.
The only theoretical reason I can see for wanting to put two double sockets on a 4.0mm spur from a 2.5mm ring would be because it was anticipated that these two sockets would be heavily loaded. That would create an unacceptable load potential on one point of the ring.
Where a number of lightly loaded outlets are to be installed then a 13a FCU spur for ease of installation would be sensible, but where more than one outlet is required and load is unknown always incorporate on the ring.
Absolutely not. Bs 7671 permits a maximum of 1 double outlet to be on an unfused spur from a ring.
The only theoretical reason I can see for wanting to put two double sockets on a 4.0mm spur from a 2.5mm ring would be because it was anticipated that these two sockets would be heavily loaded. That would create an unacceptable load potential on one point of the ring.
Where a number of lightly loaded outlets are to be installed then a 13a FCU spur for ease of installation would be sensible, but where more than one outlet is required and load is unknown always incorporate on the ring.