p11jor

Hi all did a board change today, tested before fitting new 17th board and was getting a Ze of 68.3

High 60s on my ring finals etc......

Now with Rcd protection the maxium permitted Zs is 1667 but anything above 200ohms should be investigated.

The problem is defiantly external, I isolated the supply and pulled the 1361 and tested as close to the suppliers line and onto the earth of the tnc-s system.

Thats where I was getting the high 60ohms reading. Obviously there was no power getting through into the domestic side so I disconnected the gas and water bonding also to make sure that the main earth hadnt disconnected an we were picking up some sort of earth from the gas or water. Again I was on high 60s

Popped next door (own empty property next door also) and was getting 0.13ohms.

The 68.3ohms Ze and high 60s zs's still conform according to the regs but i know in my head there is a problem externally, has anyone experienced this? What did you do?
 
DNO are obliged to maintain PME earthing at <0.35 ohms. get on the phone to their emergency dept.
 
Right then I have called supplier they are coming out. Be sometime between 7pm & like 4pm tomoz!!lol!!
yep...we`v had dealings with the DNO
on various occasions over distributers earth....with differing results/responses....some opps were ok....then there was this right obnoxious cow n all....
 

Reply to Complies but Somthing is wrong in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock