Running some calcs I'm confused about what Zs to use when calculating 5 second disconnection times.

In circuits with 1.5mm2-4mm2 cable a fault doesn't seem to pull the voltage down much at the trafo terminals so from an ohms law perspective the current magnitude reflects simple V/(R1 + R2)=I.

However I'm noticing that on mains/distribution board to distribution board circuits that the larger conductors involved (and in turn lower Z) pull the voltage down on the trafo. This means current will be lower than actually calculated? How do I approach this?
 
Running some calcs I'm confused about what Zs to use when calculating 5 second disconnection times.

In circuits with 1.5mm2-4mm2 cable a fault doesn't seem to pull the voltage down much at the trafo terminals so from an ohms law perspective the current magnitude reflects simple V/(R1 + R2)=I.

However I'm noticing that on mains/distribution board to distribution board circuits that the larger conductors involved (and in turn lower Z) pull the voltage down on the trafo. This means current will be lower than actually calculated? How do I approach this?
Zs is not r1 + r2
It is this value plus Ze, which is the effective transformer impedance

If you don't include the Ze the actual current will be much lower than any random value calculated by ignoring the transformer
 
Zs is not r1 + r2
It is this value plus Ze, which is the effective transformer impedance

If you don't include the Ze the actual current will be much lower than any random value calculated by ignoring the transformer

My apologies. I was thinking about Ze.

Ze is small relative to R1+ R2 in 2.5mm2 cable so the voltage stays near nominal at the trafo during a fault at the socket. But a fault on 120mm2 cable pulls the voltage down at the transformer terminals to half or less.
 
Last edited:
While often Ze is though of in terms of earth impedance, what matters is the earth loop impedance.

More fundamentally it is the fault current that disconnects the OCPD. Usually that is what you get from a measured Zs & supply voltage but some cases like a UPS or small generator might appear "stiff" in terms of good voltage regulation, but when actually shorted out give far lower fault current than the PFC measurement would imply.

We have a couple of makes of 5kVA UPS, one measures 2kA PFC and the other about 80A. When I am hacked off by the crappy software I am tempted to find out what the real fault level is, which I expect is close to the 80A value (which won't meet 0.4s for a 13A plug's fuse!), but so far professional sanity has prevailed...
 
I understand, but my point is that with larger circuits (lower Z) the voltage at the trafo will dip, so technically 230 volts is not an accurate number or the 80% multiplier.
 
I understand, but my point is that with larger circuits (lower Z) the voltage at the trafo will dip, so technically 230 volts is not an accurate number or the 80% multiplier.
No, as your Ze value includes the source impedance, so you are computing PFC from the supply voltage (no-load EMF) and loop impedance.

If you have a transformer impedance comparable to your total cable R1+R2 then you would see the supply volts drop to around 1/2, but then your Ze is both transformer impedance and R1+R2, so both are dropping their share.

It might not look as simple given the transformer may be far more inductive than the cable, so you would need to measure voltage and phase to get the numbers to add to the no-load 230, but they should do.
 
Last edited:
The 80% multiplier is for cable heating before the fault (i.e. assuming it runs at 70C, which is a bit high for most installations). Basically you compute your max Zs and then test your cables & supply when cold (or 20C design values) are no more than 80% of this.

True your transformer impedance might to rise as much (inductive component ought to be fairly stable with temperature), so 80% may be on the conservative side here, but for a general rule it works.

In the UK have a 0.95 factor for Uo to get the minimum voltage and so minimum PFC (not quite our -6% tolerance but close).
 
Last edited:
No, as your Ze value includes the source impedance, so you are computing PFC from the supply voltage (no-load EMF) and loop impedance.

If you have a transformer impedance comparable to your total cable R1+R2 then you would see the supply volts drop to around 1/2, but then your Ze is both transformer impedance and R1+R2, so both are dropping their share.

It might not look as simple given the transformer may be far more inductive than the cable, so you would need to measure voltage and phase to get the numbers to add to the no-load 230, but they should do.


So basically with Ze, I turn the transformer into an series reactor+resistor (in vector form?) and assume 230 volts infinite on the other side of the trafo?

That makes more sense.

The 0.8 vs 5 second time threw me off a bit... in regards to the physics...
 
The 80% multiplier is for cable heating before the fault (i.e. assuming it runs at 70C, which is a bit high for most installations). Basically you compute your max Zs and then test your cables & supply when cold (or 20C design values) are no more than 80% of this.

True your transformer impedance might to rise as much (inductive component ought to be fairly stable with temperature), so 80% may be on the conservative side here, but for a general rule it works.

In the UK have a 0.95 factor for Uo to get the minimum voltage and so minimum PFC (not quite our -6% tolerance but close).


I obtained 80% regarding coefficient C from IEC 61200-413:

1612811681613.png



My understanding is that C is derived from the voltage drop of the transformer while a L-E short circuit is occurring at the far end of a circuit inside a building.

Typically a short circuit on a 16-32 amp branch circuit will on average lead to the voltage (between the X0 & X1 of the transformer's terminals) dipping to about 80%. So at 230 volts, the measured voltage will be 184 volts. Assuming phase and earth are the same size from the trafo to the socket, the indirect contact voltage on the case of the faulty appliance will be 92 volts relative to remote earth. So going by the body graph a 0.4 second disconnection time is mandated.

On circuits over 32 amps R1+R2 is much lower ( as an example, 150mm2 cable vs 1.5mm2 cable) and as such the voltage drop is far more severe across the supply transformer.

During a fault on a 100 amp feeder, the voltage between the X0 and X1 terminals may drip down to 30% of the nominal. As such the indirect contact voltage to remote earth at the fault point will be 35 volts allowing for a 5 second disconnection time.
 
So basically with Ze, I turn the transformer into an series reactor+resistor (in vector form?) and assume 230 volts infinite on the other side of the trafo?
Basically yes, you can convert it all in to a Thévenin equivalent circuit.

That makes more sense.

The 0.8 vs 5 second time threw me off a bit... in regards to the physics...
The two are different aspects, hopefully clearer now!
 

Reply to Confused about Zs 5 second disconnection time in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
296
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top