Hi all

I am planning a CU change for assessment. My detached garage is currently fed from a 16a MCB in my CU. The garage CU has RCD protection for sockets and lights. My question: Can I run the SWA from an unprotected way in the house CU (as it is now) so that I don't have to consider discrimination between two RCD's (One in house CU and the second in the garage CU). The original installation is to the 16th edition so I am OK with bonding etc but this circuit is puzzling me.

The db T&E cable goes immediately out of the house wall to a box where the swa is terminated and runs 2 meters underground to the garage. The only reg I am thinking of here is 522.6.6 I do not know if the cable is less than 50mm from the surface of the kitchen wall that the cupboards sit on.. The CU is on an outside wall and goes down it and then through it to the box. The CU is in a kitchen cupboard. Just wanted to give all the facts so you know what i have here!

I don't want this causing problems during assessment.

Thanks in anticipation. :smiley2:

PP
 
Last edited by a moderator:
Well you'll be needing to up the mcb at the house end then if the submain cable permits (20amp)

SWA from an unprotected way in the house CU (as it is now) so that I don't have to consider discrimination between two RCD's (One in house CU and the second in the garage CU).
You can.

The only reg I am thinking of here is 522.6.6 I do not know if the cable is less than 50mm from the surface of the kitchen wall that the cupboards sit on..
So leave submain circuit in place & covered by rcd at the house & change garage rcd to BS EN 60947-3
Or
Remove t/e part of circuit & rewire with swa & move to non-rcd side of cu.
Or
Look in the BGB to see how you can negate the use of an rcd for the submain....it's all in there:wink5:
 
Having had a good look at the detatched garage CU, it has a separate TT system running to an earth rod that was not marked and I only found it by digging! So I am on TNCS with the garage having a TT sytem. This now prevents me from changing the garage RCD to a main switch. Rewiring the short T&E run with swa will be a mare as its behind the kitchen cupboards. Am I able to fit a time delayed RCD or RCBO?? in the house CU to achieve discrimination? (That will mean 3 RCD's in CU though?, if Time delayed RCBO not available)

Thanks

PP
 
Last edited by a moderator:
Oh what fun we have.

I would suggest that unless you can prove the T&E run to the SWA is more than 50mm deep then you have to have RCD protection on it. I would think that it is unlikely to be so deep as it was not a 16th reuirement. Also some say that where it runs through the wall it would also need RCD protection if not in metal conduit.

I think your options are:

Put a separate S type RCD in an enclosure next to the CU with surface wiring or trunking to the CU.
Fit SWA all the way, as we cannot see the job it is difficult to know if this is pratical.
Try and fit a third S type RCD in the CU to protect the circuit. I don't think you can get time delayed RCBOs.
Run new T&E in trunking until it goes through the wall.
FInd a different job for your assessment. :icon7:
 
Oh what fun we have.

I would suggest that unless you can prove the T&E run to the SWA is more than 50mm deep then you have to have RCD protection on it. I would think that it is unlikely to be so deep as it was not a 16th reuirement. Also some say that where it runs through the wall it would also need RCD protection if not in metal conduit.

I think your options are:

Put a separate S type RCD in an enclosure next to the CU with surface wiring or trunking to the CU.
Fit SWA all the way, as we cannot see the job it is difficult to know if this is pratical.
Try and fit a third S type RCD in the CU to protect the circuit. I don't think you can get time delayed RCBOs.
Run new T&E in trunking until it goes through the wall.
FInd a different job for your assessment. :icon7:

Thanks KFH. Some excellent points there. I am not sure the garage needs a TT system. There is no earthed metal work in there and I have a TNCS supply to the house. I would have thought the earthing could have been exported to the garage CU via the CPC in the swa. If that was possible I could then protect as outlined above and change the garage RCD to a main switch. What a pain in the ar*e! Any views?
 
Last edited by a moderator:
I would have no problem exporting the earth especially if there are no services in the garage, I should have put that as an option but it is very easy to look at the detail and miss the big picture. You need to check the size of the armour for CPC sizing but with an RCD it should not be a problem but the assessor may ask. However I did an outbuilding once with the same assumption and tested a bit of miscellaneous metal work and got a Ze of 70 Ohm had to convert to TT and bond lots of metal work I had assumed was not extraneous, I could have bolted the MET to the wall for an earth. Good luck.
 

Reply to Distribution circuit protection in the Australia area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi all, I recently moved to an older property that had a run down garage. We had this removed and a summer house put up in its place. The old...
Replies
0
Views
822
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
576
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock