I have a Duromax XP1500EH portable generator which has a 240V 50A outlet and a 240V 30A outlet. I have a 200A transfer switch on my main service panel with a 240V 50A wire connector for attaching my generator. I used this connection during IDA last week and it worked great. My question is can a 50A wire and 30A wire be connected to the transfer switch at the same time from the Duromax generator simultaneously resulting in a net 80A feed?
 
Sadly not. Its either / or as the max capacity of 15KW will be exceeded and it will trip out. 50 amps is largely the limit.
 
Thank you, I guess I need to go back to school for a math refresher! A little embarrassed I didn't figure that out myself. Think I'll blame it on my calculator! Thought I came up with a great idea. Oh well, next time.
 
I've been curious about that Duromax XP1500EH myself but if you look at the specs on it.........


........the actual running amps on it is 52.00 Amps on gasoline and 47.5 Amps on propane, what I'd be curious about though is what size is the main breaker on that thing as it doesn't specify it on the schematics, best thing you could do is call the manufacturer and ask............
 

Attachments

  • Duromax1500 Schematics.jpg
    Duromax1500 Schematics.jpg
    99.1 KB · Views: 40
I have a Duromax XP1500EH portable generator which has a 240V 50A outlet and a 240V 30A outlet. I have a 200A transfer switch on my main service panel with a 240V 50A wire connector for attaching my generator. I used this connection during IDA last week and it worked great. My question is can a 50A wire and 30A wire be connected to the transfer switch at the same time from the Duromax generator simultaneously resulting in a net 80A feed?
There’s no way you will get 80 amps out of your generator. I wouldn’t advise you to use both plugs. It’s possible that you could cross the phases
 
I have a Duromax XP1500EH portable generator which has a 240V 50A outlet and a 240V 30A outlet. I have a 200A transfer switch on my main service panel with a 240V 50A wire connector for attaching my generator. I used this connection during IDA last week and it worked great. My question is can a 50A wire and 30A wire be connected to the transfer switch at the same time from the Duromax generator simultaneously resulting in a net 80A feed?
Don't think your 80A plan will work bc the generator max at 50A. So if the draw on generator is maxed out a generator's 30A and 50A sockets, it would tripped generator breaker already. You can maxed out gen 50A or gen 30A, but not simultaneously
 
  • Like
Reactions: Megawatt

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Advert

Thread statistics

Created
alreagle,
Last reply from
raywu1688,
Replies
5
Views
2,227

Advert