Hi everyone. Im a fire alarm guy, who was qualified as a spark, over 27 years ago, to the 15th edition.

Just fitting a new alarm system into a kids nursery school, and noticed that a new consumer unit had been fitted since I first quoted the job. The spark has doubled up two 10mm earth singles to make it over the 16mm needed.

Can this be ok, or does it have to be a single cable only.

cheers in advance.

Tilly


(any questions on fire alarms I'd be happy to answer);)
 
im only in 2nd year with little expierience , but id say is ok.. cant wait to someone else awnsers nowww
 
Yes but only if both cables are identical follow the same run hence the same length, if for any reason you suspect the load isnt balanced between them then it not ok.
 
Last edited by a moderator:
agree ,I just assumed that the guy didnt want to rip out the existing cable so just improved on what was there, but he might have took a diferent route
Has to be same length usually same route as this makes sure loading is split equally the calculations of having same csa but different lengths isnt recognised by regs thus not allowed although it might be mathematically safe.
I will stand corrected but i do recall the regs have a clause about paralleling cables up and that they must follow each other and be the same length.
 
Last edited by a moderator:
The regs do comment on parallel conductors in chapter 43 section 433.4, which then refers you to other parts of the regs. Though they are really aimed at LIVE conductors, under fault conditions you need the earthing conductor to be capable of carrying the possibilty of high currents.

Technically nothing wrong with doubling up on an earthing conductor, it's like so much in the industry it's deemed not good practice. I suppose if a connection broke at a termination on the MET then it could leave the remaining smaller conductor to carry those high fault currents.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Doubling up on cables to increase csa.
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Tillywolves,
Last reply from
malcolmsanford,
Replies
8
Views
6,343

Advert