I need to run several new supplies for studios. 16mm T&E is fine for the supplies. But I'm worried the earth may not be big enough. Longest run is 12M from Meter. I could just run cable then if it fails test run 16mm earth. But would be interested to learn the calculation so I can be sure from the outset.

Thanks
Michael
 
adiabatic. but easiest way is to use 16mm 3 core SWA. that also removes the possible need for RCD protection.
 
  • Like
Reactions: 3 people
√(I² x t)/k
 
  • Like
Reactions: 1 person
SWA adds about £150, although could use 2 core and armour as earth for only small increase in cost. Had not thought about RCD for supply cable. I thought this was only a requirement for sockets. What would make this install require RCD on supply cable?

Earth is TN-S

Need to get my head round adiabatic
 
It's all relates to the installation method of the supply cable to weather it requires rcd protection
 
Just a thought, if I only need 60A to each studio I can use 16mm T&E. Similarily I could run 6mm 2 core SWA. Assuming minimum 10mm earth required, how big would armour work out to be on 6mm SWA ?
Would also need to look at voltage drop, but thinking out loud.
 
Is the supply cable buried in a wall or partition at a distance of less than 50mm. If it is then it needs additional protection.
 
  • Like
Reactions: 1 person
that's why i suggested SWA.
 
But isn't that just for sockets, you don't need this for lights, so why for supply?

The regs in this case apply to all power cables, submain, lighting switch drops, sockets, cooker. All cables require rcd protection if buried in a wall less than 50mm deep, unless they are suitably protected (metal conduit, armoured cable etc)
 
  • Like
Reactions: 2 people
Okay, looking at everything. It just makes sense to use 16mm 2 core SWA. So does anyone know how big the armour would calculate to. I assume bigger than 16mm ?
 
20.3mm copper equivilant for BS 6346 70 degree SWA and ONLY 13.5mm for BS 5467 & 6724 XLPE 90 degree.
 
use 3 core then you know it's sufficient. and as for the buried in walls<50mm deep, read 522.6.101/102. any cable
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Earth Requirement
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Michaelwgroves,
Last reply from
Michaelwgroves,
Replies
23
Views
2,744

Advert