Can anyone help, i had a new combi boiler fitted last year and they used mainly plastic fittings to make there connections, i have attached a photo below my question is where should my 10mm earth bond go , the incoming water pipe is made of lead, do i simply bond the 10mm earth to the incoming water pipe with a suitable clamp and then bridge the plastic plumbing tee to the nearest copper pipe.
any feedback would be mostly appreciated
 

Attachments

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Aico 3000
telectrix

telectrix

-
Mentor
Esteemed
Arms
looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
 
P

pc1966

Esteemed
Arms
Supporter
Assuming the existing bond is 10mm then yes, put a new clamp on to the lead pipe and run another bit of 10mm up to join the existing bonding cable. Ideally you should join them with a crimp or soldering so if any one screw loosens you don't have multiple bond wires separating.

Is there a separate bond wire to the gas meter already?
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
The torpedo is a magnetic scale inhibitor, generally required by most manufacturers for their combi boilers
Post automatically merged:

Assuming the existing bond is 10mm then yes, put a new clamp on to the lead pipe and run another bit of 10mm up to join the existing bonding cable. Ideally you should join them with a crimp or soldering so if any one screw loosens you don't have multiple bond wires separating.

Is there a separate bond wire to the gas meter already?
Why? That can be left exactly as it is, the bonding should be connected after the stopcock, not before it.
And I certainly wouldn't fit a pipe clamp to a soft lead pipe.
 
T

Tonychitty

  • Thread Starter Thread Starter
  • #5
Assuming the existing bond is 10mm then yes, put a new clamp on to the lead pipe and run another bit of 10mm up to join the existing bonding cable. Ideally you should join them with a crimp or soldering so if any one screw loosens you don't have multiple bond wires separating.

Is there a separate bond wire to the gas meter already?
Yes there is, can i not loop in and out with the 10mm earth bond with an ordinary bs951
 
B

bill01803

-
Arms
Replace the plastic tee with a compression - job done (presuming the filer is metal)
 
T

Tonychitty

  • Thread Starter Thread Starter
  • #7
Assuming the existing bond is 10mm then yes, put a new clamp on to the lead pipe and run another bit of 10mm up to join the existing bonding cable. Ideally you should join them with a crimp or soldering so if any one screw loosens you don't have multiple bond wires separating.

Is there a separate bond wire to the gas meter already?
yes there is
Post automatically merged:

looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
is a magnetic scale inhibitor,
Source URL: UK - Earthing Arrangement - https://www.electriciansforums.net/threads/earthing-arrangement.187131/#post-1633862
 
T

Tonychitty

  • Thread Starter Thread Starter
  • #8
looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
is a magnetic scale inhibitor,
Source URL: UK - Earthing Arrangement - https://www.electriciansforums.net/threads/earthing-arrangement.187131/#post-1633862
 
P

pc1966

Esteemed
Arms
Supporter
Why? That can be left exactly as it is, the bonding should be connected after the stopcock, not before it.
Really, why?

Normally I don't trust plumbing joints for electrical function even when they are all metal and should be good as I have seen oddities before.

And I certainly wouldn't fit a pipe clamp to a soft lead pipe.
That is fair enough. A strip of sandpaper cleaning up the painted copper pipe just before the stopcock would have enough for the clamp and be the best place in my opinion.

Other opinions are available, just wait...
Post automatically merged:

Yes there is, can i not loop in and out with the 10mm earth bond with an ordinary bs951
If you have the cable to do it, yes.

Usually the "best practice" is to avoid breaks/screw connections in bonding wires, though it is not actually mentioned in the BS regulations, so a screw coming loose has less impact (a bit like the guidance for high leakage CPC arrangements). So if the wire is short then you could use a crimp joint to extend it, then loop round the existing far-end clamp to your new one.

You probably don't need the far-end clamp, but easiest to leave it and it won't upset the plumber who next comes to do maintenance.
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
it won't upset the plumber who next comes to do maintenance.

where's the fun in that?
 
T

Tonychitty

  • Thread Starter Thread Starter
  • #11
looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
What if the plastic tee in the future gets replaced with a metal one, should i not put a the option of a bonding clamp after the plastic tee
 
P

pc1966

Esteemed
Arms
Supporter
What if the plastic tee in the future gets replaced with a metal one, should i not put a the option of a bonding clamp after the plastic tee
Sir, put down the plumbing and walk away solely...

Just add another clamp, extending wire as needed. Quick and easy to do, not worth the trouble of trying to re-use a clamp anyway, avoids complaints of anything else not being adequately bonded as a result. Sorted!
 

Reply to Earthing Arrangement in the Electrical Forum area at ElectriciansForums.net

Get paid faster with card payments | Go Paper Free - Save Hours | Offer Finance to Customers
This official sponsor may provide discounts for members
Top Bottom