I have recently taken over responsibility for a care home which has a 3ph supply,
Incoming phase cables are 185mm, fuses are rated at 315A and the earth is 50mm, PFC is 1.15kA x 2 and the Ze is 0.20 ohms
I have been given a PIR which was carried out last year, stating amongst other things that the Earth should be 100mm based on the calculation that the earth CSA should be Phase csa /2 ( reg 543.1.1)
If I have worked it out correctly there is another calculation which is;-
S (csa of earth cable ) = Sqrt of I squared x t / K ( 143 for copper cables)
so;-
I = 2.3kA
t = 5 secs
K= 143
sqrt of (2300 x 2300) x 5 / 143
my calcs say S =35.96mm ????? so the 50mm in place should be sufficient ??????
its many years since I've done this stuff, can anyone help and check my calcs ? or am I missing something like a life????
Regards Ian