it will contain any fires longer than a plastic enclosure before eventually the fire spreads from a metal consumer unit that is the point.
 
it will contain any fires longer than a plastic enclosure before eventually the fire spreads from a metal consumer unit that is the point.
It has nothing to do with containment. To reduce the risk of fire you remove sources of heat, oxygen or a combustable material, in this case it is combustion by replacing the plastic enclosure with metal.
 
Never assume that by fitting a metal consumer unit the risk of fire is eliminated it merely slows its progress, if a fire starts within a metal enclosure it will eventually spread and that is a certainty.
 
Never assume that by fitting a metal consumer unit the risk of fire is eliminated it merely slows its progress, if a fire starts within a metal enclosure it will eventually spread and that is a certainty.
Never said it was eliminated.
I've seen the various videos by different manufacturers, a plastic enclosure burning against a metal enclosure.
What I'm trying to say which is stating the obvious is it gives better containment against fire because it does!
I don't understand where all the negative comments are coming from ?
Always someone trying to shoot you down on this forum.
Opinions are welcomed negativity or sly comments are not.
 
Never said it was eliminated.
I've seen the various videos by different manufacturers, a plastic enclosure burning against a metal enclosure.
What I'm trying to say which is stating the obvious is it gives better containment against fire because it does!
I don't understand where all the negative comments are coming from ?
Always someone trying to shoot you down on this forum.
Opinions are welcomed negativity or sly comments are not.

Just ignore them Ian if you feel that way. I've enjoyed your input recently and seem like another knowledgeable member so stick around....you will get used to how different people post etc. :)
 
Never said it was eliminated.
I've seen the various videos by different manufacturers, a plastic enclosure burning against a metal enclosure.
What I'm trying to say which is stating the obvious is it gives better containment against fire because it does!
I don't understand where all the negative comments are coming from ?
Always someone trying to shoot you down on this forum.
Opinions are welcomed negativity or sly comments are not.
Obviously metal boards are better but if connections within are sound the material of the enclosure is probably irrelevant. I can see where you are coming from by saying in contains fire better but the point of them is to remove the source of combustion. Trying not be be negative here:)
 
Just ignore them Ian if you feel that way. I've enjoyed your input recently and seem like another knowledgeable member so stick around....you will get used to how different people post etc. :)
Wear my heart on my sleeve maybe a bit too much lee.
Enjoy reading different people's methods and theories, if I can bring something positive to the table then I will.
It's interesting how everyone interprets bs 7671 different tho which is why I believe best practice guides, iet guidance notes and on site guide are written to try and make it a bit more clearer.
However using these guides seems to be a show of lack of experience or knowledge which is frankly laughable. All relevant regulations are quoted against such information so you can cross examine against bs 7671.

This thread has gone down hill tho.
 
Last edited:
Recently had a 'discussion' with an NICEIC registered Inspector on a site I was working on.
Apparently lighting within containers containing gensets should be RCD protected. The wiring for the lighting is all surface run.
The four lights were also spidered from an adaptable box rather than daisy chained. Another non-compliance.
Zs - Ze could be used to calculate the R1+R2 of the lighting circuits.
All the boxes in the schedule of test results must be filled in with either measured or calculated values. A note should be made where calculated values are used.
His main arguments were that he had passed his 2391, had been a QS for a number of years and knew the Regs backwards.
When asked he didn't know that Chapter 6 deals with I&T, though it might be Chapter 5. Couldn't explain why lights have to be daisy chained and was sure there is a Regulation stating Zs or R1+R2 can be calculated, but couldn't find it as he had no data left on his phone.
Finally he was of the opinion that IP54 rated equipment is not suitable for use outside, that it should be IP67.
 
Recently had a 'discussion' with an NICEIC registered Inspector on a site I was working on.
Apparently lighting within containers containing gensets should be RCD protected. The wiring for the lighting is all surface run.
The four lights were also spidered from an adaptable box rather than daisy chained. Another non-compliance.
Zs - Ze could be used to calculate the R1+R2 of the lighting circuits.
All the boxes in the schedule of test results must be filled in with either measured or calculated values. A note should be made where calculated values are used.
His main arguments were that he had passed his 2391, had been a QS for a number of years and knew the Regs backwards.
When asked he didn't know that Chapter 6 deals with I&T, though it might be Chapter 5. Couldn't explain why lights have to be daisy chained and was sure there is a Regulation stating Zs or R1+R2 can be calculated, but couldn't find it as he had no data left on his phone.
Finally he was of the opinion that IP54 rated equipment is not suitable for use outside, that it should be IP67.
If you felt aggrieved by this I hope you reported it?
 
If the main fuse is 60 amp then 16mm tails are fine and don't attract a code the consumer unit being 3036 might not get a code either id no modifications are evident but the rcd matter does need a code and reg number don't just chuck the whole book at it
 

Reply to EICR 3036 board - coding - meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Replies
11
Views
504
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
707
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
949
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
451
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock