Discuss EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
If you mean the Main Earth Conductor? I found one missing on a Periodic once at a Pharmacy in Bradford, so I just fitted one and moved on. I was on wages at the time! :)
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
It is not an immediate Danger, it would take a second fault (L to E) to become so, hence a C2 potentially dangerous, Niccy don't write the rules they just like to think they do.
i'd agree with a C2 as it would require a fault ( live part to exposed part ) to present a danger.
It all depends on the circumstances No main earth not a good one most situations it would be a C2 i have come across a similar situation where there was an induced voltage of 85 volts in that scenario i would give it a C1
Another way of looking at it...is that it is a very high impedance voltage source.
So the reading depends on the input impedance of the test voltmeter.
Also, why it it doesn't present a shock hazard.
C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
You can't induce meaningful voltages into a conductor without a large number of turns in a coil and a fast rate of change in magnetic flux. Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.
Capacative coupling works in the same way a capacitor works, with the insulation between conductors acting as a dialectric.
A phantom voltage picked up by a digital multimeter is harmless.
Or a suitable highish-but-not-too-high load added between your digital meter probes achieves the same effect, i.e. a load path causing the capacitance to discharge and the phantom voltage to collapse. Someone said Fluke used to sell one.
is this some sort of homework?
caus if it aint...and your coming in here to ask what is really an open & shut scenario...like what code to be alotting this...then do you really think you should be carrying out ECRs?
Reply to EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Hi, Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated...
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...