Discuss EICR Coding query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, I have recently carried out an EICR on a big house and am struggling with coding on quite a big issue. The main tails & earth's are connected into Henley blocks, then looped into 2 separate consumer units right next to the service head/meter etc. Then there is a 3rd set of tails which go into a 100a DP main switch. Connected to the load side of the switch is a 16mm Swa which runs underground into another Consumer unit in an extension of the house. There is no connection from the MET to the swa feeding this 3rd consumer unit, hence there is no main earth connection at this board. The problem is, although it is a relatively simple fix, I have been asked to only do a report & not touch any remedials yet.obviously I know the issue needs resolving as a matter of urgency, however, as far as reporting it I am struggling to find a reg. number and code. Any help much appreciated
No fault readings on dead tests, however the lack of earth connection to this DB means no Ze/Zs and also that the RCD is serving no purpose
If that’s the case I’d probably not re energise the board after doing the tests.
remember you do not have the authority to disconnect someone’s electric supply. But you can chose not t9 re energise after testing.
Is the armour of the SWA earthed?
is the SWA 3 core?
what does the separate db supply?
Is separate db on a TT system?
pictures would help.
No, the swa isn't earthed at either end. Yes it's a 3 core with the 3rd core connected to the earth bar at the consumer unit and connected to the enclosure of the 100a dp switch at the other end. The DB supplies the lighting/small power in the extension and isn't on a TT. It's literally just missing an earth from the MET to the steel enclosure of the 100a dp switch. Like I said it's a very easy fix but I have to find the reg this contravenes and code it before doing any remedials. I'm starting to wish I'd just connected it and kept quiet ?
Reply to EICR Coding query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...