The Best Practice Guide #4 has C2 for missing/ineffective earth:
  • Absence of a reliable and effective means of earthing for the installation
  • Absence of a circuit protective conductor for a circuit, other than a lighting circuit, supplying Class I equipment
  • Absence of earthing at a socket-outlet
  • Absence of effective main protective bonding of extraneous-conductive-parts entering the premises
They only have C1 for exposed live parts or incorrect polarity.

But it is something that has to be put in writing to the client (and occupier, if different) as it is clearly a high risk of any additional fault being potentially fatal.
 
Yes, and as I say i know exactly what needs doing to put it right. I just have never come across a board with no main earth connection so am struggling to find the appropriate reg/code.
You need to forget the fact that it's a board, you have a circuit (the supply to the board) without a cpc. Therefore ADS is not being met. The Zs is too high and there is no earth fault protection. Code 2.
None of the final circuit from the board will have acceptable Zs or disconnection times. All code 2.
 

Reply to EICR Coding query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
445
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
589
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
917
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock