I would C1. Either fix it there and then or do not re energise.
Discuss EICR Coding query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Couldn't even get tester to run a test as there was no connection to earth. No bonding from that board so couldn't even get a reading using parallel pathsWhat Zs did you get.
You need to forget the fact that it's a board, you have a circuit (the supply to the board) without a cpc. Therefore ADS is not being met. The Zs is too high and there is no earth fault protection. Code 2.Yes, and as I say i know exactly what needs doing to put it right. I just have never come across a board with no main earth connection so am struggling to find the appropriate reg/code.
The RCD will still provide additional protection where required. You still need a CPC to meet requirements for ADSand also that the RCD is serving no purpose