If a 63a rated RCD gets a C3, then a lot , if not most, new populated boards supplied now would warrant a C3 the minute they are fitted.
I would say that if a board comes with 2 x 632 RCDs then that is as manufactured and attracts no code whatsoever. The 63a refers to the current that it can interrupt without being damaged, if it trips with say 100a flowing through it, it will more than likely get damaged and have to be replaced. But it would have done its job.
Thermal damage to any components in a CU, not just RCDs would require at least C2, so that’s not really relevant.