Looking to run some power to my shed, my metre cupboard is opposite my shed 5 metres max, I have a smart metre and DNOs isolator, if I replaced the DNOs isolator and put a new 3 way metal unit in there so I’m changing the isolator like for like and then I’ll just feed an MCB from bottom of isolator and then my SWA to my shed? Consumer unit is too far away to feed it from there.
Thanks
 
So your main house CU would then be fed from the new 3 way one?
 
  • Agree
Reactions: Baddegg
You cannot remove the DNO’s isolator.
Is there room for a couple of henleys and split the tails coming out the isolator?
 
So your main house CU would then be fed from the new 3 way one?
Yes, I have no room to fit an enclosure at min and add Henley blocks etc, so I’ll replace the isolator with a new 3 way enclosure, in there will be a isolator which will feed the CU in the house and will add an MCB from bottom of isolator and feed my shed
[automerge]1582309452[/automerge]
You cannot remove the DNO’s isolator.
Is there room for a couple of henleys and split the tails coming out the isolator?
Nope no room, I’m swapping like for like can’t see there being an issue
 
You aren't replacing like for like. You are changing an isolator for a dist board.
 
  • Agree
Reactions: Baddegg
I’d ask the DNO before touching their equipment mate, they don’t mind you pulling fuses but removing they stuff is pushing it I’d say?..
 
  • Like
Reactions: DPG
You aren't replacing like for like. You are changing an isolator for a dist board.
Which is exactly the same just a bigger enclosure will still have isolator
[automerge]1582309856[/automerge]
I’d ask the DNO before touching their equipment mate, they don’t mind you pulling fuses but removing they stuff is pushing it I’d say?..
I see what people are saying hence why I asked, I could possibly move the isolator higher and fit some Henley blocks but those cupbords aren’t the biggest
 
Whatever advice you get on here mate, end of the day it’s still they equipment, I’d always check with em first
 
I’d ask the DNO before touching their equipment mate, they don’t mind you pulling fuses but removing they stuff is pushing it I’d say
they put in there so you dont pull the fuse if their is any upgrade of a consumer
either swap the original board or find another solution .
 
  • Agree
Reactions: Baddegg
Think I have a better way, I have a socket in front room with is directly opposite shed, if I punch through the wall and fit a fused spur (13A) then SWA to my shed? I have already have the 3 way consumer unit so can I just feed that to my consumer unit I have 63A 30mA RCD and 16A, 6A MCBs obviously I’m only governed by 13A which all I want is a couple sockets and a light
[automerge]1582311502[/automerge]
Can I feed the 63A 30mA RCD with the 2.5mm SWA?
 
Think I have a better way, I have a socket in front room with is directly opposite shed, if I punch through the wall and fit a fused spur (13A) then SWA to my shed? I have already have the 3 way consumer unit so can I just feed that to my consumer unit I have 63A 30mA RCD and 16A, 6A MCBs obviously I’m only governed by 13A which all I want is a couple sockets and a light
[automerge]1582311502[/automerge]
Can I feed the 63A 30mA RCD with the 2.5mm SWA?
Is the circuit already RCD protected?
 
Is the circuit already RCD protected?
No it’s not
[automerge]1582312781[/automerge]
So can I feed the 2.5mm to 63A RCD? Protected by 13A fuse?
 
Last edited:
Not sure why you are asking - the 63A is the maximum rating of the RCD, and is not some rating that it will trip at (it will just overheat or weld the contacts etc if you put more than 63A through it).

So 2.5mm2 cable is fine from a protective device of 13A (the FCU fuse), assuming the short cable length you mentioned.

Remember to gland the SWA and earth the armour.
 
If you are feeding it with a 13A fused spur from the front room socket, you could use a 13A RCD fused spur instead.
 
pointless feeding a CU from a RFC socket. just add a RCDFCU, then SWA to shed socket/s, 5A FCU for light/s, fed from shed socket circuit.As SWA does not require RCD protection, the RCDFCU can be in the shed
 
  • Like
Reactions: richy3333 and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Electric metre cupboard
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Bradley6969,
Last reply from
telectrix,
Replies
15
Views
2,142

Advert