L

lokesh.dee

HI

I have a MCC panel it is showing KW reading for each phase L1,L2 and L3 are 4.7KW,4.0KW and 4.2 KW repectively. the energy consumption for 2 hours was 16 Kwh.how come it is possible

my doubt is my load was stable for 2 hours with 10-15% variation i should be 8-10 Kwh for 2 hours why it is 16??do we have to consider sum of 3 phases power??? or average of them??
 
If you are reading KW on each phase then for 3Ph it the sum of the phases. Just be sure you are reading KW or KVAr on all meters.
 
  • Like
Reactions: 1 person
thank you!!

I am sure that it is K W . if it is sum it should be 24KWH for two hours right??!! because the load was stable for 2 hours
 
there is energy meter installed in the panel i wanted to compare the kw and kwh reading so i have asked this generel question

tell me in generel total KW of a motor = L1KW + L1KW + L1KW


if it is the case where we can find supporting theory??
 
You need to take efficiency and power factor in to account. The KW rating of a motor is the output at the shaft.
 
  • Like
Reactions: 1 person
While a 3 phase motor running which is connected to particular panel kw reading is showing only for one phase l 1. My doubt is on energy meter why that is showing only one ohase kw ??!!!
 

Similar threads

S
Replies
15
Views
2K
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
electrical energy calculation in 3phase
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
lokesh.dee,
Last reply from
lokesh.dee,
Replies
8
Views
1,240

Advert