Hi everyone.

I have an emergency light test coming up. I have never carried one out before. Is it as simple as:
1. Checking there is a key switch/isolator
2. Making sure all emergencies are working correctly
3. Making sure the batteries are up to scratch by them staying illuminated for the 3 hours?

Any advice will be great fully received.
Thanks
 
Well first step is a good read of the bs5266....but the paperwork is just as important...logging and numbering every fitting, with location and type. Covering log book for customer and maintenance tests, of visual, weekly 5 mins tests, 6 monthly 30 min tests and annually 3 hour duration discharge test...you will need to have spares onboard, for lamp and battery changes, there is no "i`ll come back next week to change the tube", it needs to be done asap....a survey before testing is always important
 
  • Like
Reactions: 3 people
Apparently there was a test done with remedials outstanding and they still haven't been done. So that's a good start....
 
Can be a very serious game to play.....if for any reason it can be prove that lack of em lighting, resulted in people being trapped in a building...the HS could have a field day....always keep log book and paper work up to date
 
  • Like
Reactions: 1 person
Thanks for the advice. Is the testing side basically switching the key switch and making visually checking all fittings are up to standard?
 
erm no from memory you are seeing if there is a compliant system. if the building is massive and has one emergency light would you say that was fine? do you have to original design documents?
 
No they won't be there I wouldn't imagine. And I would imagine the system is old so could well need a few adding.
Do either of you know of anywhere I can download a decent cert template?
 
Well it is valid point, if there is not enough lighting to comply, you will need to re design/upgrade the system....as to certs, used your scam jobbies,
 
Is the testing side basically switching the key switch and making visually checking all fittings are up to standard?

Unfortunately, not every system includes a keyswitch to mimic a power loss. I was working in a nursery last week and had to go in at the weekend as the circuits had to be switched off to do a visual check :-(
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
emergency light testing
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
CSP2012,
Last reply from
Duncan Bennett,
Replies
8
Views
1,774

Advert