Can somebody please advise?

We recently had our gas meter moved to a box outside our house after the service was found to be leaking. The company that did it have sent somebody round to do the bonding from the new gas outlet pipework to our fuse board but the route he's said he has to take I really don't want him to do as this would mean drilling more holes, I've had enough of the amount of disruption this job has caused already. A friend has mentioned they could do it by installing an earthing rod and wouldn't need to go through the house, is this possible?
 
In 1 word NO

The whole point of equipotential bonding is that all "surfaces" are connected to the MET / fuse board.

Not sure your friend understands this.
 
I would agree with the above an earth rod would make thing possibly more dangerous rather than safer.

There may be alternative routes for the cable to take to get back to the main earth terminal. If the gas was already bonded and the meter has not been moved far then perhaps running a short cable and joining on to the old bonding cable would be less disruptive. Another option would be to run a cable outside the house if there is a route available.

An additional consideration is that if the gas meter has been moved and a new supply pipe has been installed then it is likely that this pipe would be MDPE (yellow plastic) and the gas meter may no longer require bonding as it may not be an extraneous part, however this would need to be verified and it is often difficult to convince gas installers that bonding may not be necessary.
 
The bond could follow the route of the new gas pipe to where it is connected to the existing if that would help ,and if the gas meter and the CU were in the same cupboard the problem is solved.
 
Can somebody please advise?

We recently had our gas meter moved to a box outside our house after the service was found to be leaking. The company that did it have sent somebody round to do the bonding from the new gas outlet pipework to our fuse board but the route he's said he has to take I really don't want him to do as this would mean drilling more holes, I've had enough of the amount of disruption this job has caused already. A friend has mentioned they could do it by installing an earthing rod and wouldn't need to go through the house, is this possible?
This nonsense comes from those who think the requirement is to earth the gas service, bonding is a different thing altogether and your friends suggestion will actually increase the danger bonding is intended to reduce. As already suggested, if you can get verification that the new service is plastic bonding may not be required.
 
Even if you do need to bond it, you should do it where the copper pipe enters the building, although gas people prefer to see it in the meter box. Doing it where it comes inside might save a bit of drilling.
 
Can somebody please advise?

We recently had our gas meter moved to a box outside our house after the service was found to be leaking. The company that did it have sent somebody round to do the bonding from the new gas outlet pipework to our fuse board but the route he's said he has to take I really don't want him to do as this would mean drilling more holes, I've had enough of the amount of disruption this job has caused already. A friend has mentioned they could do it by installing an earthing rod and wouldn't need to go through the house, is this possible?

I take it your friend is not an electrician then!

Hope you get it sorted without too much disruption.
 

Reply to Equipotential Bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi all, our summer house had a FuseBox consumer unit fitted last year and the guy who did the work has retired. nothing wrong with the install...
Replies
8
Views
901
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
403
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
584

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock