Discuss Error message when taking Ze reading, any thoughts? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

robd

-
Arms
Reaction score
339
Guys, was doing an earth fault loop test earlier with a Megger multifunction tester. Got an error message after a few beeps. Have had problems in the past with the same message and found to be a loose earth somewhere on the circuit, any thoughts on what else might be causing it. Circuit concerned is a lighting circuit, emergency lights and pendants combined, about 10 lights in all. Connections made by a.n.other, can go back and check them all if there's no other way :confused:

Cheers
 
Are you testing on Hi or No trip loop test???

Most likely a probe issue although I think you get a 'trip' message if a probe looses contact.

Have you checked the manual???
 
Last edited by a moderator:
Guys, was doing an earth fault loop test earlier with a Megger multifunction tester. Got an error message after a few beeps. Have had problems in the past with the same message and found to be a loose earth somewhere on the circuit, any thoughts on what else might be causing it. Circuit concerned is a lighting circuit, emergency lights and pendants combined, about 10 lights in all. Connections made by a.n.other, can go back and check them all if there's no other way :confused:

Cheers

You're testing Zs then, not Ze.:)

If you're testing on the switch-live, it is switched on, isn't it?

Lack of voltage will abort the test also.
 
Yes Z's :). It's not a switch live it's the live feed into the last light, initially thought it was probe losing contact but tried 3 or 4 times with the same result, did it from the switch to make sure good contact. Could dig the manual out, I think it comes on a disk rather than paper hence why I haven't done so yet.

Lenny it's on no-trip as on a 17th board.

Cheers
 
try it at home? or on another cct to rule out probes & tester? also try with skt adaptor on a ring cct? this will also rule out CU. then try again on light cct in question on no trip on tester if an rcd in cct. also make sure you have a good contact on terminals. use all three leads on tester too. think i read another post regarding 6A mcb tripping on this test before???
Cant quite remember??
hope this helps
 
Yes Z's :). It's not a switch live it's the live feed into the last light, initially thought it was probe losing contact but tried 3 or 4 times with the same result, did it from the switch to make sure good contact. Could dig the manual out, I think it comes on a disk rather than paper hence why I haven't done so yet.

Lenny it's on no-trip as on a 17th board.

Cheers

Are you using three leads - this is required for no-trip.

I suspect if you've tried it at the switch you are only using two leads (unless the install loops at the switch)
 
Yeah it's a DP switch for a loft light so did use all three leads, was wondering if maybe one of the leads had come disconnected, sometimes they pull out...don't think it was, only one lead that could've come out would be the black lead otherwise the polarity signs would've flashed up...am back tomorrow for another look
 

Reply to Error message when taking Ze reading, any thoughts? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi everyone, I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth...
Replies
14
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top