Clipped direct ceiling level and into the attached garage lights will be mounted on the joists, so RCD is required.

Can I fit a RCD/RCBO to a old fuse board? (NOPE)
 
Last edited by a moderator:
All is good then :-)

1. Bonding
2. Rose Or Junction box to spur
3. No RCD required
4. Test & Inspect
5. Certificate

Did I Pass :-)
 
Last edited by a moderator:
All is good then :-)

1. Bonding
2. Rose Or Junction box to spur
3. No RCD required
4. Test & Inspect
5. Certificate

Did I Pass :-)

lol...if the JB is above a ceiling and not accessible it will have to be maintenance free.
 
Cheers, I might be able to come of the rose :-). (Very Grateful of the replies and help)

As for the bonding, the gas main and water are about 5m away from the CU, I have to bond 600mm or less at the incoming pipe correct?,
 
Off topic GEelecs but out of interest how long was your domestic installer course?
 
Have you tested the EFLI at the point you plan to extend the circuit from? I have
Have you considered how a fault in the garage would affect the rest of the installation, and whether this is acceptable or not?
How are you going to clip direct from a ceiling rose which is presumably in the centre of the ceiling? And does your customer really want a clipped cable in their living room
 
Cheers, I might be able to come of the rose :-). (Very Grateful of the replies and help)

As for the bonding, the gas main and water are about 5m away from the CU, I have to bond 600mm or less at the incoming pipe correct?,
Main bonding needs to be at, or as near as practicable to, the point of entry of the extraneous part to the installation.
 
Hello LEE,

5 weeks on and off, I'm learning still and yes I have low experience I know this!!.

We all have to start somewhere in life to get somewhere we want too.

G
 
Hello LEE,

5 weeks on and off, I'm learning still and yes I have low experience I know this!!.

We all have to start somewhere in life to get somewhere we want too.

I do agree with the last sentence but do you think 5weeks is adequate? Do you have someone you can call upon to work along side you to gain some experience?
 
I haven't tested the earth fault loop impedance at the point of extension.

I consider a fault in the garage light will take out the lights in the house as they are on the same circuit.

I will be running the cables above the ceiling, clipped to the joists
 
I haven't tested the earth fault loop impedance at the point of extension.

I consider a fault in the garage light will take out the lights in the house as they are on the same circuit.

I will be running the cables above the ceiling, clipped to the joists

Is there insulation above the plasterboard ceiling?
 
I'm currently looking for someone to build experience with, I have all test equipment and its calibrated all the required books and low experience.

I'm an engineer at work installing 1/3 phase x-ray systems.

No 5 weeks wasn't long enough and I know in my own mind I'm not experienced enough that's why I'm starting small, I'm enjoying it and I want to learn more.
 
I haven't tested the earth fault loop impedance at the point of extension.

I consider a fault in the garage light will take out the lights in the house as they are on the same circuit.

I will be running the cables above the ceiling, clipped to the joists
How do you know that the extension to the circuit will comply with ads?

So its not straightforward clipped direct then? Is it a loft above? If not how do you plan to gain suitable access to the joist to clip it?

Are you insured to carry out this work?
 