I know we all instal fan isolators but is this just a habit or a necessity. Could a double pole switched fcu be used instead, feeding a permanent live and a switched live via a pull coard? Just a thought or have I missed something?
 
A recent very long winded post discussed this very subject. Do a search and you will find the answer. Well you will find lots of different opinions anyway lol.
 
I agree it all boils down to manufacturers instructions and they all say three pole isolation and 3 amp supply but if a permanent live and a switched live were fed from a FCU and the neutral that surely incorporates both isolation and fuse in one unit.
 
You could even feed it from a 3 amp MCB, doesnt matter where abouts on the circuit it is. But the question is, can you safely isolate a FCU?
 
The advantage of installing a 3 pole isolator is that all supplies are isolated in one action , whereas a fused spur isolating the permanent live and another switch isolating the switched live could lead to confusion with isolation ,
With ducted in line fans in loft spaces and remote areas to the room that its in , I feel its always best to provide local 3 pole isolation nearby to the fan , providing a local means of isolation ,
 
The advantage of installing a 3 pole isolator is that all supplies are isolated in one action , whereas a fused spur isolating the permanent live and another switch isolating the switched live could lead to confusion with isolation ,
With ducted in line fans in loft spaces and remote areas to the room that its in , I feel its always best to provide local 3 pole isolation nearby to the fan , providing a local means of isolation ,

So if I was to supply two line conductors from a FCU one permanent direct to fan one via a switch then to fan, if I switched off FCU both line and the neutral would be isolated. Or is running two conductors from a single terminal on a FCU wrong ?
 
I am losing the plot with this. If it's a ducted, in-line fan, or any other fan for that matter, who exactly is going to need to isolate it??? If it's a sparky who has been called in to look at it, then he will make sure its properly isolated before he/she looks at it, who else should be needing to work on it?? They are all class 2 anyway.
 
Habit and handy. Although strictly speaking ive never believed they are required by 7671, manuf instructions may ask for one but im unsure if they would ask for local. Although nearly all ask for a 3A fuse. I used to fit decent fans that didnt require them.

As for a fused spur for isolation, remove the fuse, seems its deemed good enough for isolation with a fuseboard with removable fuses, also MK fused spurs can be paddlocked with the fuse carrier out, unsure if that would be DP but you have always got the MS!
 
This is how I would install isolation for timer over run fans , I personally install 3 pole isolators , so as the fan can be isolated leaving the lights still in use , The fused spur controlling the light and fan with a 3 A fuse would isolate the live feeds to the fan , and fuse can be removed ,,
 
Last edited by a moderator:
It's a switch. Too high for compliance with building regs. 450 - 1200. Got pulled by Warwick BI. Wouldn't listen to my opinion that above door made sense
 
It's a switch. Too high for compliance with building regs. 450 - 1200. Got pulled by Warwick BI. Wouldn't listen to my opinion that above door made sense

Haha BCs making it up as they go. if you are installing non lockable isolation it should be under the control of the person working on the equipment so it could be on the ceiling. its not a functional switch and using it as such would break building regs anyway.
 
Not too sure about building regs? but an isolator can be used for functional switching (BGB P149) .....

I agree it was more from the point of veiw of a overun fan being fitted and installing a function switch to turn it off, pointless the isolator is there for isolating.
 

Reply to Fan isolators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all new to the forum Learning the trade as an improver, trying to get my head round something. When taking a feed from the light switch to...
Replies
10
Views
363
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
460
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top