thanks tazz.
a bit confused..why i have to fix fire alarm panel on the shop..shop its independent from other premises..there its a meter room..where its the best place for them.. But they form the same building, if there is a fire in the shop, the flats above are at risk. Again risk assessment needed to confirm.
when you say '' and a zone per level of each flat landing area '' did you mean each floor to be on independent zone ..i thought shop to be one zone and other premises one zone..in total two zones..Firefighters need to know on entering a building where the fire is, One zone covering 4 floors, and another covering a shop store room etc. Will not really give then a chance. Technically, the staircase itself is another zone, under BS, but this is usually ignored in smaller conventional systems, as it becomes confusing on the zone map
you say just smoke in hallway and heat d in kitchen..what about bedrooms..its enough for one bedroom flat..The main requirement for dwellings is Grade D LD2 consisting of circulation areas , such as hallways, landings. Plus risk areas, such as a kitchen. There is no requirement for detection within a bedroom, unless LD1 is requested.