Hi all, I have been called out to a fire alarm that has two faults on two different zones, the problem is that there are some devices that I can not find . new plaster board ceilings have been put in and stud walls have been built over the top of the alarm. What I am going to do is go right back to the panel and start tracing cables as far as I can then disconnect the cables that I don't need if it is in the middle of a circuit I will just run a new cable in i need to do a lot of tracing would a tone generator work in this situation
 
All devices must have access for servicing, and this should have been thought out before work commenced. There must be a plan of schedule works and drawings to follow. If lower ceilings have been installed, then depending on the new assessment, the voids above may need detection. If walls have been added or remove, again more detection maybe required. This sounds like a real boggit & scarper job.
A tone tracer will not work on FP200, as the cable is screened.
 
Last edited:
Sounds like a rip it out and start again job. Like Tazz says, there has to be access to ALL devices and if the ceiling has been dropped, depending on the size of the void you may need detection above as well as below the new ceiling.

To me, sounds like a typical "sod it, the fire alarm isn't important. Build over rather than have it adapted" job.

Also, you don't say what system it is? You may find if its an addressable system, you can pretty much work out the rough cable run depending on the device text related to the address but this certainly isn't a fool proof way of doing things. Addresses don't have to go in any sort of order! (although logically you would)
 
just thinking here. tone genny wil work on the cores but only if you are tracing at detectors/sounders where you can get at the exposed cores.
 
just thinking here. tone genny wil work on the cores but only if you are tracing at detectors/sounders where you can get at the exposed cores.
Without seeing the job it sounds like a new installation would be the better option.No doubt the client will throw there arms up in the air in mock horror but remeber your name will be on the certificate
 

Reply to Fire alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
659
Hi All, Might be a stupid question but I have about 30 of these smart+guard alarmed call point covers to deal with. All the batteries are dead...
Replies
0
Views
482
Can someone please guide me on this? I have virtually no experience of home alarm systems. The client has an alarm which had been fitted to her...
Replies
17
Views
1K
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
Replies
5
Views
857
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock