Proposed plan to supply from 32mcb on main csu in 4mm t/e approx 15m to outside wall into adaptable box -then 4mm 3 core swa to Garage approx 10m.
Inside garage - new csu rcd protected 16A x1 and 6A x1.
From 6A run 1.5 t/e to garage light and switch. From 16A run 2.5 t/e to 2g socket in garage. from socket 2.5 t/e to adaptable box at rear of garage and 2.5 3core swa 5m to summer house.
Adaptable box in summer house then run 2.5 t/e to 2g socket, from there 2.5 t/e to Switched FCU to suply light in 1.5 t/e. From first FCU 2.5 t/e run to second Switched FCU with 1.5 t/e to Adaptable box and then 1.5 3core swa 5m to supply garden lamp post.

Can anyone see any problems with this plan please. Also main house is TT and would i be best terminating earth at garage abd sinking its own earth rod making Garage a seperate TT.
 
if the house is TT there is nothing to stop you adding another rod at the garage. it may even bring the Ze down on the house. i would check your possible loading and calculate volt drop as well. other than that, if your 4.0mm T/E from the CU to adaptable box is buried in wall, you will need a RCD or RCBO at the CU. this will do away with the need for RCD in ngarage, but, if there is a fault, it will trip in the house.
 
if your 4.0mm T/E from the CU to adaptable box is buried in wall, you will need a RCD or RCBO at the CU. this will do away with the need for RCD in ngarage, but, if there is a fault, it will trip in the house.

The 32A mcb is on rcd protected board already and the 4mm t/e is under a suspended floor to the nearest air grate to the garage
 
As suggested, add another couple of rods to your TT system, it will indeed reduce your final Ze if then connected to your existing TT system. Just make sure they are driven deep, (not close to any building walls) and protect the cable to rod connections with purpose made ground boxes and with say amalgamating tape around the connections...
 
if you are coming off an RCD in the house , then fitting another on the garage, you won't have discrimination, so in case of a fault. one or the other , or both, will trip. better to feed from non RCD section of house CU if you can, if not, leave out thr RCD in the garage.
 

Reply to Garage and summer house supply (tt or not) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
668
Hi all, I recently moved to an older property that had a run down garage. We had this removed and a summer house put up in its place. The old...
Replies
0
Views
849
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
771
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
765

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock