Discuss Help!!!!!!!!!!!!!!!!!!!!!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.
why do you need a seperate earth to make rcd,s and rcbo's work?:confused: an rcd will actuate at around 22-30 milliamps, either of the phase conductors could come loose and touch exposed metal work which would allow the cpd to work,(connected to cpc or not),..... surely as scotty mentioned its a minute inbalance that would trip them....earth leakage that is. Non rcd/rcbo cpd's would require cpc for sure. Hope i'm not missing the point here:)
everyone is a bit right - and some are a bit wrong here.
An RCD does not need an Earth per se, but needs an EARTH PATH
it is quite conceivable to have a house with no incoming earth, but there would be an alternaive path though the CPC to the MET, through the protective bonding and down to earth though any extraneous conductive paths (gas, water pipes etc)
as long as that path is 1667 ohms or less, the RCD would trip before the fault voltage reached the magical 50V, and even with a path of 7666 ohms or less would still trip.
Of course we need an earth path for CPD's to work correctly, but an RCD, with ANY path to earth as stated above, will trip off
and before anyone starts thumping the keyboard, I am NOT suggesting using an RCD means you dont have to have an incoming earth:p
Tr25 you say he has done his 17th, 17TH what ??Joint before Breakfast!! (and I'm not talking crimped)Anything without an earth return becomes a special location that is not allowed under normal circumstances, ie domestic installations
Listen mate im on your side lol.Hes a wee know it all ---- who has done a 17th course and is spouting out all this crap all the time.trouble is he is so sincere about it half the guys at work are starting to believe him.He is adamant the new regs say that if the board is protected by an rcd or if individual circuits all have rcbos then there is no need for an earth because the rcd/rcbo will operate on the imbalance of live and neutral.
ok, I have explained how an RCD COULD work without an incoming earth with an extraneous path of 7666 ohms or less (but probably not in the required time), but that is an accidental by-product of there being no earth in the first place
How the hell does this guy think ADS will be achieved:eek:
I teach 17th edition, and this guy is talking utter tosh
he has no doubt misenterpreted something he was told on the course
along the lines of RCD protected circuits only needing a Zs of 1667 ohms or less for their 60898 MCB's etc etc
If you want to 'douse his flames' a little, ask him for the relevant regs numbers to back up his 'theories';):p
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?
Luke
I agree it will trip if the phase and neutral currents are not the same, however I would not sign off an installation without an adequate earth path unless it was SELV for instance You sure this guy isn't on about bonding? not done my 17th conversion yet but there was take about there not being a requirement for bonding in bathrooms anymore
bit more complicated than that Moog, for bathrooms, but yeah, if all conditions are met, then no supplementary
O.K. it seems that there is some agreement on the workings of an RCD on this post.
An RCD protects by constantly monitoring the current flowing in the live and neutral wires supplying a circuit or an individual item of equipment.
The supply and the load are both connected to EARTH
Under normal circumstances, the current flowing in the two wires is equal. When an earth leakage occurs due to a fault in the circuit or an accident with the equipment, an imbalance occurs and this is detected by the RCD, which automatically cuts off the power before injury or damage can result.
If there is an imbalance in a circuit protected by the RCD, the leakage current has got to be going somewhere. If there is no earth path to take the current to earth, what is going to take it there? a person who recieves a shock from live metal work? :eek:
I think your friend should study the 16th Edition before trying the 17th Edition.
Like I said Warren, there may be an 'accidental' earth path through any extraneous paths, which, if 7666 ohms or less, would still allow the RCD to trip, but it is most defintely NOT in the 17th that you dont need an inscoming earth because of it:p
I think your mate is confusing a Main supply earth and equipotential bonding. The 17th does not require you to install equipotential bonding to pipes such as a bath room basin as long as the circuits in the bathroom are protected by an RCD. Every installation must have a main earth.
Sorry, meant supplimentary bonding not equipotential.
shakey, i understand about the 1667 ohms bit, but, shouldnt it be lower than that (exact figure not known at mo) to do away with an unreliable earth path??
Reply to Help!!!!!!!!!!!!!!!!!!!!!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...