Hi All,

I would like to ask for help for my project. My boss ask me to put an warning lamp when the load current reach 300A.

The condition:

-Crushing stone motor runs with unstable current (fluctuated).
-Fluctuating range (100A-250A) normal condition.
- Need to install indication warning lamp n buzzer when the load current reach 300A without stopping the motor (dont want the circuit breaker).

Really need some help here. Thanks.
 
Use a current sensing relay with alarm outputs.
Possibly may need a brief time delay if the peak current may reach 300A for seconds without problems.
Output of the relay will supply the lamp and buzzer.
Assuming 3 phase motor and equal current in each phase choose the relay for the appropriate current on one phase.
 
Hi Rich I was looking at this thread earlier and was on the EATON site looking for CT sensors, bit noticed that the largest they do were 200amp

I noticed that the ones you linked to were also 200amp do they do a 300amp?
 
400/5 CT feeding a current relay with adjustable hysteresis setting. I got the relay from RS when I did exactly the same job. The CT was from D. K. Moriarty (honest!)

Sherlock Holmes
 
Agree ^^^
Sorry Malcolm I was not looking into it in detail just giving the idea so the project could be planned; I can't readily find in the UK 300A current sensing relays however CT are available up to very high currents and so could be used to provide a reasonable output if the direct sensing is not available.
 
A 5VA 400/5A will do it nicely. Still got the drawing kicking about somewhere if the OP drops me a PM. I used the same system to control the infeed to a crusher.
 
Use a with alarm outputs.
Possibly may need a brief time delay if the peak current may reach 300A for seconds without problems.
Output of the relay will supply the lamp and buzzer.
Assuming 3 phase motor and equal current in each phase choose the relay for the appropriate current on one phase.


Thanks Richard. Helpful information.
 

Reply to High Current Indicator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Had one today I can’t get my head around. 4Kw motor connected to an Allen Bradley soft start. The panel runs 2 motors Both 4kw. I was called...
Replies
2
Views
704
Last weekend I experienced a weird electrical fault with my 2010 Peugeot Boxer Van. A little background - the van is a 2010 Boxer 330 2.2 Short...
Replies
3
Views
870
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top