This week I nearly learned a hard lesson re this!! (using a Lutron RA2 inline dimmer to control 6x 700ma 13w LED fittings)
So I thought 6x 13w=78w- thats fine its well within Lutrons stated 150w of LED load.
But after having issues with the dimmer- Lutron told me it has a 1amp load max. (6x 700ma= 4.2a so its too load)
But I put my clamp meter on the line cable coming out the dimmer when the 6no lights were on and it was only pulling 0.3a AC (78w/230v=0.3a)

What is the correct way of working out current when in comes to DC lighting?

So I managed to split the circuit into 2x 3 fittings and the driver had dip-switches to change the ma output- so I ran them all at 250ma (so both Lutron dimmers with 0.75a load and so far so good)

I am seeing more and more 350ma/700ma/1050ma LED fittings on the market- but how are they being controlled with dimmers?

For example:

say if they was 10x of the above on one circuit (14w, 1050ma)- how can it be controlled as one circuit?

This can handle the wattage but can it handle the current? (rated at max 2.2a)

Cheers
 
This is mighty confusing. The Lutron dimmer is dimming the 230V AC, right? In which case the 700mA current on the ELV DC output side of the driver is neither here nor there, the ELV circuit is not passing through the dimmer. It's the 0.3A AC input to the driver you measured that has to be within the dimmer's 1A limit. The AC input current to the driver is always going to be lower, sometimes much lower, than the DC output current. Therefore I think the problem is compatibility, not overload.

Are you sure the drivers are the phase-angle controlled versions (I see Lucent offer various options including non-dimmable, DALI etc.)
 
Last edited:
This is mighty confusing. The Lutron dimmer is dimming the 240V AC, right? In which case the 700mA current on the ELV DC side of each driver is neither here nor there, the ELV circuit is not passing through the dimmer. It's the 0.3A AC input to the driver you measured that has to be within the dimmer's 1A limit. The AC input current to the driver is always going to be lower, sometimes much lower, than the DC output current. Therefore I think the problem is compatibility, not overload.

Are you sure the drivers are the phase-angle controlled versions (I see Lucent offer various options including non-dimmable, DALI etc.)
Thanks
These are the drivers
 
I think I have a better understanding of this now!
So on the driver it will state a input current (so for the drivers in hand it is 0.15a) (this is the AC side- which the dimmer is concerned with)
I have 6x drivers so a total of 0.9a- so I should be under the Lutron RA2 inline dimmer max limit of 1a

Do I under stand it better?

However it was causing the dimmer to go into fault mode- I have since split the circuit in half (1x dimmer with 3x fittings and another dimmer with the other 3x fittings- and it has been ok so far..)
 
Yes, the driver AC input current must be within the dimmer's current limit, and as a separate deal the power must be within the dimmer's power limit. Exceed either of those and it might physically fail / burn out. But you seem to have had a compatibility issue where although both the current and the power were within the stated limits, it still didn't work correctly until you divided the load up. LED drivers are complex beasts relative to the humble filament and can have all sorts of specific behaviours that can cause dimmer malfunction. It seems a common experience that some pairings of dimmer and driver simply don't play nicely together even when you stick within the specs.

That is one of the annoying things about phase-angle controlled drivers and dimmers, and in truth is a symptom of using a technology designed for one purpose (dimming filament lamps) for something it wasn't originally designed to do (remote controlling LED drivers.)
 

Reply to high current LED lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm not an electrician so I need help! I thought this would be a fairly straightforward job but there's so many options, I don't know...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock