Discuss High Ze on TNCS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
coxyboy
I did a test on a domestic property today.
the Ze I measured was 0.60
this is above the maximum permitted that is 0.35 for a tncs system.
I coded it a c2 as the Ccu was a 17th edition dual rcd type.
do I have to notify the electrical supplier of this high reading? And have I coded it right?
any help would be very greatful. Thanks
if they won't come out what do I have to do? Is it my duty as being the last electrician on site to get this sorted ASAP ?
Ask to speak to the duty engineer otherwise you'll spend an hour trying to talk technical to someone who doesn't actually give a damn.
it needs sorting. phone DNO and ask for the duty engineer. nobody else will have a clue. they have a duty to maintain the earthing at 0.35 or less
Assuming the test leads and tester are ok? Have you confirmed the result with a second tester wouldn't want to look a idiot :wink_smile:
Reply to High Ze on TNCS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
4K