coxyboy

I did a test on a domestic property today.
the Ze I measured was 0.60
this is above the maximum permitted that is 0.35 for a tncs system.
I coded it a c2 as the Ccu was a 17th edition dual rcd type.
do I have to notify the electrical supplier of this high reading? And have I coded it right?
any help would be very greatful. Thanks
 
Thanks
if they won't come out what do I have to do? Is it my duty as being the last electrician on site to get this sorted ASAP ?
 
Ask to speak to the duty engineer otherwise you'll spend an hour trying to talk technical to someone who doesn't actually give a damn.
 
it needs sorting. phone DNO and ask for the duty engineer. nobody else will have a clue. they have a duty to maintain the earthing at 0.35 or less
 
Assuming the test leads and tester are ok? Have you confirmed the result with a second tester wouldn't want to look a idiot :wink_smile:
 

Reply to High Ze on TNCS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
891
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock