I have garden lights in the front and back gardens. They are on a timer.
When the garden lights are on and the indoor house lights are also on, everything is fine.
When the Garden lights are on and I turn on the oven or ( occasionally) other large heating appliance, the entire property electrics trip. When I isolate the the garden lights (ie isolate them on the main switch board) everything works completely normal. The cooker works fine in the daytime and evening providing the Garden lights are not on. Please advise.
 
N to E fault, probably in the lighting circuit, the large load (on another circuit) causes enough current to bypass the RCD via this fault.
 
Sounds like you have a single RCD protecting the entire installation? How many circuits are involved?

Picture of the consumer unit may help advise further, but probably needs an electrician with suitable test equipment to test the circuits and track down the guilty party.

What you've managed to do so far will be very helpful in guiding where to test (garden lighting looks like the first place to check).

If you want to do more troubleshooting, If the front/rear garden lighting can be easily split then you could narrow it down to front or back and then carefully check wiring/junction boxes for water ingress or damage.

It does sound like a fault on the garden lighting - it may not be enough by itself to reach the limit and trip the RCD (It may be 15mA and the RCD might trip at 23mA, for example) - The cooker or other load may then add enough in combination with the lighting to trip the RCD.

Having a single up front RCD is not ideal for this very reason, so reconfiguring or upgrading the consumer unit with an RCBO for just your lighting circuit, or some or all of the other circuits, may be a good long term investment - depending on any test results you could seek advice or quotes on that if you want to be sure the problem tripping will not reoccur.
 
It sounds like several factors all contributing a bit.
Heating elements are common for earth leakage especially if they are getting older.
Anything where water ingress is possible is another prime candidate for this kind of fault.
I was then typing similar stuff to @Dartlec, just read his very good post!
You are going to need someone with accurate test equipment unless there is an obvious cause.
 

Reply to Household Electrics Tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
895
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock