Yes, and it should be practically the same as L-N or L-E since N, E, and true Earth should be within a few volts of each other.
Whether you can do that safely though is another question, would depend on the setup you use to measure and how well you understand it. As always, never make assumptions: always treat every conductor as if it is live and dangerous until proven dead!
Provided that the star point of the transformer that the line conductor is coming from is referenced to earth then yes, Which is the case with UK power distribution
So if you were to measure between line conductor of a socket in your house and a rod stuck into some soil, you should see a voltage between to two
Here is a simple drawing to show how the circuit is completed
I’d like to think I’m not one of them
Just remember fate conspires against us .
( Especially the more educated ! )
.... Warning signs == half your garden is concrete/tarmac....
If the results are nowhere near 0V ..listen for the sound of a nearby neighbours water feature ..with no RCDs ;)
Reply to If you drive a metal rod can you use it as a reference to measure voltage in the UK Electrical Forum area at ElectriciansForums.net
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Assuming that you measure the windings for a power transformer, for example: A-B: 2,258 ohms B-C: 2,262 ohms A-C: 2,250 ohms, how do you...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...