Hi guys rewiring an immersion heater from a double pole 20amp switch, circuit is wired in 2.5mm t+e up to DP switch. What are peoples thoughts on using 1.5mm flex the regs state that this is capable of carrying u to 16 amps ,would prefer to use 2.5mm flex but can not find a 20amp dp switch with a flex outlet to take a 2.5mm flex ...

circuit is on 16amp breaker and flex run is about 1 metre.

Thanks
 
Yep the butyl 1.5mm is the best choice as has been stated, it has a greater heat tolerance and won't break down at the Imm' heater terminals due to the heat.
 
Which reg relates to 'pushing it'?

Hi

No reg relates to pushing it, i personally dont like running cables near to their maximum, some heat resistant cables have a ccc less than 16 amps some more, also i like to derate due to ambient temp. So 2.5mm runs cooler, less volt drop, better thermal constaints etc. I never said 1.5mm couldnt be used, it depends upon the cable and other factors.

You all have your preferences and veiws, some a little emphatic, i have mine.

Cheers
 
Last edited by a moderator:
Hi

No reg relates to pushing it, i personally dont like running cables near to their maximum, some heat resistant cables have a ccc less than 16 amps some more, also i like to derate due to ambient temp. So 2.5mm runs cooler, less volt drop, better thermal constaints etc. I never said 1.5mm couldnt be used, it depends upon the cable and other factors.

You all have your preferences and veiws, some a little emphatic, i have mine.

Cheers

The tabulated values in the regs book are not the maximum for the cables, they are already worked out to avoid running the cables at their maximum!
All you do by applying the 'I don't like running near the max' approach is to end up wasting money.
Plus the ratings are already at 30degrees so to apply a factor for normal room temperature in this country would actually increase the ccc.

Plus of course the terminals on an immersion heater and cable grip are designed for 1.5 so using bigger cable often leads to broken cable clamps and poor terminations
 
The tabulated values in the regs book are not the maximum for the cables, they are already worked out to avoid running the cables at their maximum!

All you do by applying the 'I don't like running near the max' approach is to end up wasting money.
Plus the ratings are already at 30degrees so to apply a factor for normal room temperature in this country would actually increase the ccc.

Plus of course the terminals on an immersion heater and cable grip are designed for 1.5 so using bigger cable often leads to broken cable clamps and poor terminations

Hi

Which tabulated values are they dave? i think you will find they are max values, reference a table please.

Well Dave the life span of a cable reduces the higher the temp, waste money, i dont think so, i bet the I2R losses would easily pay for the bigger cable.

Those little cupboards get toasty with a big copper radiator an ambient temp of 35 C is prudent dont you think?

Your clearly using inferior elements, go for quality.

Cheers
 
Hi

Which tabulated values are they dave? i think you will find they are max values, reference a table please.

Well Dave the life span of a cable reduces the higher the temp, waste money, i dont think so, i bet the I2R losses would easily pay for the bigger cable.

Those little cupboards get toasty with a big copper radiator an ambient temp of 35 C is prudent dont you think?

Your clearly using inferior elements, go for quality.

Cheers
Looking at table 4F3A, which states current-carrying capacity (no mention of minimum or maximum). I note the current carrying capacity of flexible cables (single phase & non armoured) for 1.5mm & 2.5mm to be 16amp & 25amp respectively. The table does not submit an ambient temperature for those particular figures. However, does start to give rating factors for ambient temperatures from 35'c.

It also provides rating factors for 110'c, 150'c flexible cables, 35-80'c x 1 & 35-120'c x 1 respectively, i.e. no effect on current carrying capacities for those cables at those temperature ranges.

If we are to assume the ambient temperature of an immersion heater cupboard to be 40'c (i'e just measured mine at 33'c), a rating factor of 0.82 would apply.

Therefore, a standard flexible cable of 1.5mm & 2.5mm, would have capacity of 13.12a & 20.5a. Heat resistant flexible cables would not have their capacities, affected by this particular ambient temperature.

I see that some heat resistance flexes are sold as heat resistance to 85-90'c range.

My observations are; standard flexible cables would be at or above their limit, in terms of their current carrying capacities in the above scenario, whereas heat resistance would not. To use 2.5mm heat resistance flex for 3kw immersion heater, is not necessary whereas 1.5mm is more than sufficient.
 
Last edited:
Looking at table 4F3A, which states current-carrying capacity (no mention of minimum or maximum). I note the current carrying capacity of flexible cables (single phase & non armoured) for 1.5mm & 2.5mm to be 16amp & 25amp respectively. The table does not submit an ambient temperature for those particular figures. However, does start to give rating factors for ambient temperatures from 35'c.

It also provides rating factors for 110'c, 150'c flexible cables, 35-80'c x 1 & 35-120'c x 1 respectively, i.e. no effect on current carrying capacities for those cables at those temperature ranges.

If we are to assume the ambient temperature of an immersion heater cupboard to be 40'c (i'e just measured mine at 33'c), a rating factor of 0.82 would apply.

Therefore, a standard flexible cable of 1.5mm & 2.5mm, would have capacity of 13.12a & 20.5a. Heat resistant flexible cables would not have their capacities, affected by this particular ambient temperature.

I see that some heat resistance flexes are sold as heat resistance to 85-90'c range.

My observations are; standard flexible cables would be at or above their limit, in terms of their current carrying capacities in the above scenario, whereas heat resistance would not. To use 2.5mm heat resistance flex for 3kw immersion heater, is not necessary whereas 1.5mm is more than sufficient.

Hi

I find this a strange remark, 1.5mm is a minimum and with some cables inadequate. Unnecessary means excessive, so what is excessive about installing 2.5mm cable, the cost, crikey?

Ill give you some pro's, you give the con's

Lower operating Temp
Less Volt Drop
Lower I2R
Can be used as a supplemetary bonding conductor
A longer life span
More Robust
Pretty much all flexible cables even derated will be okay.

Cheers
 

Reply to Immersion Heater in 1.5mm flex in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if you could help please. I'm looking to fit a BG IP66 external socket mainly for occasional jet wash/vacuum usage and...
Replies
9
Views
1K
Hi all just here as an enthusiastic learner/diyer to gain knowledge and help on bits and bobs At the moment I am confused I have a new single...
Replies
20
Views
3K
Hi chaps Customer has asked me about installing a mains supply to a 16amp UPS on their server. The UPS hasn’t come with a power cord, the...
Replies
2
Views
839
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock