i have just been to look at a job where i was asked to install a cooker as the previous one had nearly burned the house down apparently. When i took the cooker out there was a large burnt patch (300m accross), loads of charcoal, almost got through 1/2" ply below . When i pulled out the heat resistant flex i couldn't see where it had been plugged into, but it's likely it was plugged into the ring. It is a 3200w cooker from argos, the customer had got an argos technician out and apparently the cookers fine and it was down to the installation. Customer reckons it was sat ontop of the connections and it was bodged up, i did try asking the customer to clarify how the cooker was connected up, but couldn't get much out of her! Theres a 2.5 t&e running below the worktop behind the cupboards, not connected to anything but still live? But couldn't find where it came from as all the cupboards are full to the brim!

It's only a small house, 2 up 2 down, it's tt, got a 100ma rcd upfront and a 8 way 3036 board with 3 circuits (ring, lights and shower). Ze is 5-6ish ohms. Would it be ok to spur it off the ring to a fused spur above the worktop, and then down to the cooker? An just put it on a minor works?
I'm not entirely sure what the line is about working on a circuit without 30ma rcd protection, do i need to add an rcd first or not?

Also, the voltage is 250v at this house, 3200w at 250v is 12.8, so it i put a 13a fuse in the fcu then it will be alright? I seem to remember something from college saying all calculations to be worked out at 230v, in which case the current will be 13.9a and it will be more than the fuse rating. Probably never blow, but what should i do here?



i would suggest that your priority would be ( as well as compliance with any relevant regs ) to protect the client and the property from any future mis-adventure, as well as yourself, so, as you don't know what's within thew walls,
fit the rcd as standard practice !!! Why chance ? Your job is'nt as a croupier in a casino or a game of chance, if you have any doubt at all, always aire on the side of caution and protect,protect,protect........ Yourself included.
 
12.8 or 13.9A ? a 1361 fuse will hold well above 13.9 Amp for evermore! Fuses are not overload devices! - they are for short circuit protection. I wouldn't dream of putting a cooker on 2.5mm cable, or even a spur off a ring - cookers should be separately fed as they can affect the diversity factor for the ring. I know it's only a wee cooker ( almost camping size!),
but what happens when the lady decides she would like a bigger cooker? She might go back to Argos!
 
As long as you surface wire it and make sure it is a FCU and not a socket outet you will not require an RCD. However, I would advise you make note of this on the cert. Always have your onsite guide mate, its very handy. Remember this job will need to be notified as its work in a kitchen ( special location ) Good luck!!
 
seems backwards to me, i explained to the customer what the situation so she could liase with the DNO direct and she was just baffled with terminology and started panicking when i said theres no incoming earth. hows she supposed to explain to the DNO what the problem is if she doesn't know herself? i'll speak to the customer again tomorrow and explain the hold up.

All you have to do if you are feeling like helping, is what I do...
Get customer to phone DNO and say "I don't understand all this rubbish and want you to talk to my electrician. I hereby authorise him/her to act on my behalf in this matter".
You then phone DNO and sort it out. Works every time for me. :)
 
Keep reading - that para only covers cables in steel conduit or with metallic protection, look on next page under diagram where it talks about circuits that are not in steel conduit or are unprotected - 30mA RCD is required for ALL circuits.
(Sorry, forgot to post quote with this and it came from an earlier page, re-OSG page 28)
 
I think the only way to settle this post is for us all to meet up at a centrally located pub, have a quick drink, and then fight it out in the car park!

We could all bring our OSG and BGB and use them as weapons!
 
I think the only way to settle this post is for us all to meet up at a centrally located pub, have a quick drink, and then fight it out in the car park!

We could all bring our OSG and BGB and use them as weapons!

My BGB is encased in a titanium folder....Bring it on.... :13:
 
Electricity northwest eventually changed the cutout for a PME one, and i have the customer agreed to a new board and a new cooker circuit. installed the cooker circuit just now and tested it, but the oven(brand new) is getting extreemly hot at the bottom, so i have disconnected it and told them i'm going to have to have a look into it.

heres the pictures from when it set onfire the first time
IMG_1489.jpg

IMG_1490.jpg

and the flex i removed, customer said originally it was because of the way it was wired up that i got too hot and the oven was sat on the JB, but i don't think thats possible as heres the flex i removed, not melted and looking in good condition. there was far too much copper on show, and no use of a flex clamp but i don't think that started the fire.
IMG_1488.jpg


and before installing it i turned the lower plinth thingy round so there was not charcoal showing like so:
IMG_1491.jpg


i've read through the instructions, no mention of an air gap below needed. whats your suggestions? gonna phone the manufacturer tomorrow anyway
 
i've just cooked my tea, unscrewed the oven and pulled it out and it was red hot too, but there was a 20mm gap between the wood and the metal oven, whereas theis cheapo argos oven just sits on the wood! what about new bit of wood, with a load of 20mm holes in it for cooling? i can't really sit in on 2 spacer to make an air gap as theres only so much room below the worktop.
 
well i've decided the best people to speak to are the local kitchen fitter shop, I reckon a new base, drill a load of 25mm holes in it, and fix some louvre vents to the front and back so air can circulate below the oven. hopefully that will do the trick
 
Surely that oven must be faulty. The inner oven spaces are covered with insulation.
Doesn't seem right that the outer casing is getting that hot to burn the surrounding woodwork.
 

Reply to in after a cowboy, cooker nearly burnt the house down! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
820
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock