Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation resistance test to earth at 500v got 10Mohms to earth on all phases run is about 50mtrs?
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

littlespark

-
Arms
Esteemed
Advent Win
What is it connected into at the board that’s made off? Thinking you’re reading through equipment.

Either that, or the cables damaged somewhere
 

Pete999

-
Arms
Esteemed
Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation resistance test to earth at 500v got 10Mohms to earth on all phases run is about 50mtrs?
You mean INSULATION resistance test Mate surely
 
T

Toneyz

  • Thread Starter Thread Starter
  • #9
Has the mccb got a vgi add on the bottom?
If so you may just of nackerd it
So used to using Eaton so maybe you could let me know what this vgi is, please.
 
T

Toneyz

  • Thread Starter Thread Starter
  • #11
As far as I am aware it's an Earth Leakage add on block
Not as far as I know a standard MCCB they don't do them in S.P. range is NSX MLG2.2 if that helps it has CT metering but as I posted nothing on end (load)
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Did you try drying the exposed surface of the insulation between the bared ends of the cores and the gland? 10MΩ could just about be caused by condensation.

I think 'vgi' should read Vigi, Schneider's trade mark for their residual current add-on actuator.
 

telectrix

-
Mentor
Arms
Esteemed
wasn't vigi the artificial intelligence in Star Trek 1?
 

Pete999

-
Arms
Esteemed
wasn't vigi the artificial intelligence in Star Trek 1?
No Tel Vger, As voyager with the oya erased after centuries of exposure to cosmic space dust and radiation, Crikey don't you anything?:tongue::);):D:rolleyes:o_O lol
 