hiya, got 2 new circuit which all have led gu10's on them, led strip etc. on a 6amp b mcb, seems to be tripping the mcb intermittently, not the rcd. Most of them are controlled by dimmers, just wondering if they got a high start up current. Would it be worth sticking on a type c? Anyone had any issues like this? There is no squashing of cables behind the switches. Thanks
 
I've had issues with type b mcb's before but it was sockets not lights. It was all to do with the inrush and they were too sensitive. Try a type c and see if it solves it
 
I've had issues with type b mcb's before but it was sockets not lights. It was all to do with the inrush and they were too sensitive. Try a type c and see if it solves it


Earth loop impedance first and refer to bgb (80%) to make sure circuit still complies.
C is half max zs of a B.
Boydy
 
hiya, got 2 new circuit which all have led gu10's on them, led strip etc. on a 6amp b mcb, seems to be tripping the mcb intermittently, not the rcd. Most of them are controlled by dimmers, just wondering if they got a high start up current. Would it be worth sticking on a type c? Anyone had any issues like this? There is no squashing of cables behind the switches. Thanks
if you are dealing with inrush....
then why the hell would you think the RCD would let go?

christ..
 
hiya, got 2 new circuit which all have led gu10's on them, led strip etc. on a 6amp b mcb, seems to be tripping the mcb intermittently, not the rcd. Most of them are controlled by dimmers, just wondering if they got a high start up current. Would it be worth sticking on a type c? Anyone had any issues like this? There is no squashing of cables behind the switches. Thanks

Several questions spring to mind.
1.Have you carried out IR tests?
2.Why are you looking for 'squashed cables behind switches'?
3.Have you tested the RCD,it may not be functioning causing the MCB to operate on a fault?However a fault will have been discovered on the IR tests you have already done...right?
4.How much load is on the circuit...have you done a load test with a clamp meter?
5.Does the mcb only trip on switch on or in use?....it is simple to check for inrush current issues,switch the MCB off...turn on all the lights...switch MCB on,if there is a high inrush it will trip as you switch it on.(Only after eliminating all of the above)
 
Last edited by a moderator:

Reply to intermittent tripping on 2 new circuits with led lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
524
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
389
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock