Discuss IR Testing - Whole Consumer Unit....? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

Jamie

Hi,

It says in BS7671:2008(2011) Page 95 10.3.3 ii that "When testing simple installations, i.e. those consisting of one consumer unit only, the installation could be tested as a whole with all fuses in place, switches and circuit beakers closed, lamps removed and other current-using equipment disconnected"

So this means there is no maximum to how many circuits are in this "consumer unit" and no limit to how many can be tested at one point??

This means I could go into a house for example, with one consumer unit and test this way, because to me a domestic 10 way board is a "simple installation"...right?

What's the maximum amount of ways in a C/U before sparky's start to class it as not a simple installation??!?!

(I test each circuit individually, but I would like to know this as it is very grey area and doesn't make a lot of sense, why test each circuit when it says this!)

Thanks
Jamie
 
No such thing as a "simple installation". You could only do a global IR test on a new install where you knew every electrical point on it as any other install could have sensitive equipment or other appliances still connected that you are unaware of.
 
if you do a global IR on a board and get a reading of, say, 100Mohm, you know that each final circuit will be better than this and testing individually won't really give you any worthwhile additional information. Obviously, if you do a global test and the result is, say, 2Mohm, you might want to investigate further to identify the poor circuit(s).
 
Global IR testing is fine for preliminary testing such as fault finding or reassurance if needed , but deffo not with RCDs on the board and care has to be taken with any equipment still connected to the circuits , remember this is only for initial verification purposes, you would still need to test individual circuits as per the test schedule either for installation certs or EICR
 
if you do a global IR on a board and get a reading of, say, 100Mohm, you know that each final circuit will be better than this and testing individually won't really give you any worthwhile additional information. Obviously, if you do a global test and the result is, say, 2Mohm, you might want to investigate further to identify the poor circuit(s).

You couldn't be more WRONG!!
 
OK, on a 230V installation. I do a global IR on 10 circuits and get 100 Mohm. Then I do individual IR testing and get a range of values from 120 Mohm to 450 Mohm. What action would you take as a result of obtaining the additional figures?
think resistances in parallel,that's why you'd get a difference between a global IR test and individual circuits,thats why it's best just to do a global for initial checks and fault finding.
 
think resistances in parallel,that's why you'd get a difference between a global IR test and individual circuits,thats why it's best just to do a global for initial checks and fault finding.

Resistances in parallel, OK, I understand that. But if you've already determined that all final circuits have an IR of at least 50 times the required value, what is the merit in proving that some of them are actually, say, 100 times the required value?
 

Reply to IR Testing - Whole Consumer Unit....? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

D
I've booked in an electrician to run an EICR, I have an old unit here, whilst searching for quotes one guy said it looks ok and may not need...
Replies
6
Views
1K
One of our contractors has identified a concern with multiple showers on a single 100 amp supply.(unsure how many yet i have asked for further...
Replies
3
Views
197
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
740
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock