If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician
As some of you guys know my week end project still on the go. Turns out family owner of house now requires an island worktop /cupboards in the kitchen. In the island 1 x oven and 1 x hob (both electric) and LED lights in kick board. I'm wiring 2 X cooker circuits. I know an induction hob will be installed but don't know the loading. I propose to install 2 x 45A DP switches above the worktop on main wall as per norm. Appliances will be with the 2m rule (if in fact it that rule still exist). My question is, what is the best method / practice to get the cooker cable from switch to island via u/g. Underfloor heating be installed, overall depth of floor is 175mm incl insulation which has not been installed as yet. I was thinking of 6mm 6242Y cable enclosed in some pvc flexible ducting (ploy duct or similar) .The LED lights same way but from a sw/spur.
 
Would have thought underfloor heat and PVC flexible conduit not a good mix
 
  • Like
Reactions: 1 person
Would have thought underfloor heat and PVC flexible conduit not a good mix

Not only that love to see the cable calcs for the cables with it being buried in the floor with underfloor heating and insulation?
 
  • Like
Reactions: 3 people
wet heating or electric? if insulation is going below the heating, then if the cables( in a duct ) are a few inches below that, should not be a problem.
 
Would have thought underfloor heat and PVC flexible conduit not a good mix

Yes..know what you mean..........ducting /cable will be on concrete slab insulation on top then heating pipes. As underfloor heating, the heat will be spread over a large area therefore the actual temperature will not be high. hopefully guys on here that are use to wiring kitchen islands can steer me in the right direction. Many Kitchens are done this way. I've not done any.
 
wet heating or electric? if insulation is going below the heating, then if the cables( in a duct ) are a few inches below that, should not be a problem.

It's a wet system run off an ASHP. That's another story!
 
There's some pretty flash looking power poles available, can't you supply the circuits from above?
 
1 x 10mm t&e cable in 25mm steel conduit to a single 45a switch on island , then 2 6mm cables from switch to each appliance.
easy peasy.
;-)
 
  • Like
Reactions: 2 people
What about his lights?
 
That'll be 100mm insulation plus 75mm concrete on top probably.
Typical temperature of the water in U-floor is 40c.
The underfloor pipes won't be laid under cupboards or the island.

Lay the duct on the concrete and clip it down or it will move, then the insulation can be laid over the top of it.
 
  • Like
Reactions: 1 person
That'll be 100mm insulation plus 75mm concrete on top probably.
Typical temperature of the water in U-floor is 40c.
The underfloor pipes won't be laid under cupboards or the island.

Lay the duct on the concrete and clip it down or it will move, then the insulation can be laid over the top of it.
Hi,you cannot guarantee this,as proper calcs and install for wet U/F,is ALL the floor area with margin at perimeter. I know,this depends on situation and installer,abroad,and where it has been used for generations,they do this,then insulate where not wanted/required,such as cupboards. Installing wet U/F is a major task,and is only done correctly,either new-build or retro,in conjunction with other design features,insulation being the biggest consideration. Kitchens are swapped and changed many times during a properties life,and to design a wet U/F system just to suit one,present kitchen,would be short-sighted. Anywho...i digress,it should be possible to design some type of ducting,to facilitate your required cabling needs,regardless of U/F pipe runs.:conehead:
 
  • Like
Reactions: 1 person
I'm doing a kitchen on thurs and fri this week, has an island too.

He has channelled out a slot about 6" wide and 3" deep, Its going to have pipes in one compartment and a few cables in the other, they will be spaced apart so I would imagine it will be fine.
 
I'm doing a kitchen on thurs and fri this week, has an island too.

He has channelled out a slot about 6" wide and 3" deep, Its going to have pipes in one compartment and a few cables in the other, they will be spaced apart so I would imagine it will be fine.

Property I'm working in, has Block & Slab (is that correct term) Basically solid concrete beams with blocks inserted between them. I'd better not chop the concrete beams, the owner might be a tad upset.
 
There are means of providing a safe complying electrical installation for just about every building situation encountered. Sometimes you'll need to think outside the box as they say, but i have yet to find myself in a position of being stumped and unable to find a suitable solution to a site based problem.

Bringing in an electrical supply for a kitchen island with a wet underfloor heating system must have been encountered time and time again throughout the land, so shouldn't be too much of a problem to solve between the relative trades on site....
 
  • Like
Reactions: 1 person
Agreed,the closest spacing i have ever seen,between pipework on an U/F heating system,still leaves room for a cable of sufficient size to power an oil rig! If the floor is Bison block and beam,or similar,as it sounds,provision for entry points is relatively easily achieved BEFORE screeding. Afterwards,breaking out,or coring can bring serious problems. I attended a job with a pal who had built a barn conversion extension,and used block and beam for the lounge and kitchen. The plumbers had core drilled (Hilti diamond rig) for an island sink unit.Months later,the island had cracks around it,and a big crack had appeared around the window lintel 3 meters away. I broke out the air brick to get a look in the void,as only 300mm space. They had core drilled through the middle of a beam,this had fractured and dropped,which explained the movement in the island,but because of its' length,it had levered up the inner course of blockwork where it sat,and lifted it to point where cracks were evident in the bedroom! This was yet another occasion where we got to find out the total and utter waste of time,that the NHBC scheme is...hang on...a scheme not working?...sounds familiar...:hammer:
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
island in kitchen
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
driverman,
Last reply from
PEG,
Replies
17
Views
4,408

Advert