Was it caught by a screw/nail? Or just a lack of grommet?
The the look of it, plasterers float. It was at a socket where a plasterer has been working. Grommets in the back box so it’s all I can think only would be.
[automerge]1597757315[/automerge]
Was it caught by a screw/nail? Or just a lack of grommet?
[automerge]1597757247[/automerge]
Hopefully new RCD, short fixed and all happy once more!
Yep,new rcd working correctly now too. ????
 
So what exactly was happening when that faulty circuit was energised? Was the MET swinging up to 230V and the gas pipe remaining at true earth? If all the earthing and bonding is OK elsewhere, it would also have been connected to a Ze of 48 ohms and dumping 5A into the ground. If it wasn't a solid short (hard to tell from your '0.00', which if it meant megohms, could still be 10k.) then why was it having such a marked effect at the MET?

What I'm getting at is that it's nice to find a fault, but unless one can prove that it was directly responsible for the symptoms, there could be more to find.
 
So what exactly was happening when that faulty circuit was energised? Was the MET swinging up to 230V and the gas pipe remaining at true earth? If all the earthing and bonding is OK elsewhere, it would also have been connected to a Ze of 48 ohms and dumping 5A into the ground. If it wasn't a solid short (hard to tell from your '0.00', which if it meant megohms, could still be 10k.) then why was it having such a marked effect at the MET?

What I'm getting at is that it's nice to find a fault, but unless one can prove that it was directly responsible for the symptoms, there could be more to find.
It was a dead short live to earth.
 
What was the actual resistance, or did you see the conductors physically welded together?
 
0.00 what? Megohms on an IR test? If so, that can still be 10kΩ which is more consistent with a carbonised insulation fault and is far from being a dead short, and shouldn't have much impact on the system elsewhere. If it's 0.0Ω (which you can't tell from an IR test, needs to be low ohms) then the only reason you were able to close the breaker was that the entire earthing system throughout the installation became fully live WRT real earth. Anywhere in the middle, the fault would have got much hotter.
 
It looks more like a nail than float damage. If so, until you released it, the nail could have had an affect on your readings. As Lucien asks, we’re you continuity or IR testing?
 
From an IR reading on a MΩ scale you can't say whether or not it was a dead short, only that it was not more than tens of kΩ. It could be 10,000 times higher than what one would really consider to be a short, although it sounds like it probably was from the other evidence.
 
0.00 reading on the mft.

MFT's have a variety of different ranges so just staying 0.00 could be ohms, megohms, volts, amps, milliamps, seconds.

An electrician should understand the need to, and be able to, quote the units as well as the measurement for the measurement to actually mean anything at all.
[automerge]1597770499[/automerge]
These were IR readings.

Then you haven't measured a dead short, you have measured 0.00 megohms which could be many thousands of ohms.
Depending on your exact tester if you had switched your tester to the normal resistance range it may have given a result suggesting that it was open circuit.
 
0.00 what? Megohms on an IR test? If so, that can still be 10kΩ which is more consistent with a carbonised insulation fault and is far from being a dead short, and shouldn't have much impact on the system elsewhere. If it's 0.0Ω (which you can't tell from an IR test, needs to be low ohms) then the only reason you were able to close the breaker was that the entire earthing system throughout the installation became fully live WRT real earth. Anywhere in the middle, the fault would have got much hotter.
I did state in the photo I posted that it was 0.00 IR between L/E.
[automerge]1597772032[/automerge]
MFT's have a variety of different ranges so just staying 0.00 could be ohms, megohms, volts, amps, milliamps, seconds.

An electrician should understand the need to, and be able to, quote the units as well as the measurement for the measurement to actually mean anything at all.
[automerge]1597770499[/automerge]


Then you haven't measured a dead short, you have measured 0.00 megohms which could be many thousands of ohms.
Depending on your exact tester if you had switched your tester to the normal resistance range it may have given a result suggesting that it was open circuit.
In my original post I stated that I had end to end continuity on L N & E. So now I’ve seen the damaged cable, that to me that would suggest that the live and earth are touching together/fused together, however you choose to name it. That was the baffling thing,I had continuity of the ring. When I got to the job,I didn’t have a lot of spare time. I knew I had to go back and replace the RCD anyway which was faulty. So I disconnected the circuit which was causing the gas pipe to become live, leaving the site safer than when I arrived.
 
Last edited:
I'm afraid this is pedantry, but it's important pedantry. I have an insulation tester for HV circuits that measures in gigaohms. If I said it read 0.00 would you consider that to be a 'dead short'? Even though it could be ten megohms? Would you have guessed I was talking about gigaohms and not megohms? Always state the units!
[automerge]1597774407[/automerge]
the circuit which was causing the gas pipe to become live

230V between gas pipe and MET could be either way round - how do you know that the gas pipe was not remaining at earth potential and the whole earthing system of the house was becoming live? From my reading of the evidence I would say that is more likely. I'm not criticizing here, just looking at other technically valid interpretations of the data that you've posted.
 
Last edited:

Reply to L-N Reverse and 240v on gas pipe in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
394
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock