Gents

I have an issue with my lighting circuit upstairs. Truthfully I have caused it myself but I am hoping some of you guys will have an answer.

1) refurbing bathroom, removed walls and removed light switch and ceiling rose from both the separate bathroom and toilet room.
2) all upstairs bedroom lights were working when a rogue cable (labelled in diagram) was connected up with the remainding twin cable and 2 single reds.
3) Disconnected the rogue loose cable and lost all upstairs lighting.
4) connected it up as shown in diagram and bedroom 1 and 2 lights work, bedroom 3 does not. Havent got as far as putting in bathroom ceiling rose yet.

Any advice and direction would be appreciated.

Diagram attached

Cheers
Kane
 
How many cables do you have left at your bathroom ceiling rose?

If i was to hazard a guess, I would suspect your supply for bed 3 is looped off your bathroom ceiling light as part of a 3-plate wiring system. When the fitting in the bathroom is up, i would expect your light in bed 3 to come on.

I'm guessing your 'rogue' cable was the supply for upstairs lighting and you have interupted the circuit somewhere in the middle with the bathroom light? Giving you some lights on and some lights off.

hope that helps
 
Hi Hobsoni

Thanks for reply! I currently have no bathroom ceiling rose. I actually have exactly what is in the diagram. The 'rogue' cable was connected up amongst the cables in the diagram. What do you think the single red cables are doing?

Cheers
Kane
 
Is this diagram showing?
View attachment 15340
Gents

I have an issue with my lighting circuit upstairs. Truthfully I have caused it myself but I am hoping some of you guys will have an answer.

1) refurbing bathroom, removed walls and removed light switch and ceiling rose from both the separate bathroom and toilet room.
2) all upstairs bedroom lights were working when a rogue cable (labelled in diagram) was connected up with the remainding twin cable and 2 single reds.
3) Disconnected the rogue loose cable and lost all upstairs lighting.
4) connected it up as shown in diagram and bedroom 1 and 2 lights work, bedroom 3 does not. Havent got as far as putting in bathroom ceiling rose yet.

Any advice and direction would be appreciated.

Diagram attached

Cheers
Kane
 
Hi Hobsoni

Thanks for reply! I currently have no bathroom ceiling rose. I actually have exactly what is in the diagram. The 'rogue' cable was connected up amongst the cables in the diagram. What do you think the single red cables are doing?

Cheers
Kane

Now i have seen your diagram (dunno why it weren't there before??).........I'm actually with drew35 on this one, not quite sure what is going on. Without digging yourself any further, have you taken down the fitting in bed 3 to see whats behind there? If you got 2 red singles going to bed 3 (and the light worked prev) then one of em has got to be a neutral.

If in doubt don't touch owt!
 
Your mixing up switch lines and lives.... As suggested get your local ''Trusted'' electrician in to sort out your dilemma, as trying to explain things out to you, will/could be exhausting on a forum. ...It'll not cost you much and give you peace of mind that all is well with your electrical installation....
 
Hi mate looks like the rogue cable as you say is part of the main loop in and out and your 2 seperate single reds are the switch lives
But i cant be certain loking at the diagram as it isnt the best

as others have stated if your not sure what you are doing best get a electrician to have a look as he will be able to trace the cables
it would have been better if you had drawn a diagram of the way the fitting was connected prior to removal
a common mistake by DIYers

if in doubt get an electrician out lol

good luck
 
Hi Brucelee.

I am intending to get an electrician. Although, as I am on my lunch break and really curious to understand what is going on is there anything else I could maybe tell you in order to give you more to go by?

Sorry about the rough paint drawing lol.

Cheers
Kane
 
As my learned friends say, get someone out. It won't take an electrician long to sort this out and even if said spark is expensive you're still looking at change from £50. How much change is debateable mind you but at least you'll know it's been done right
 
Disconnect all the cables take out fuse / mcb

Remove all lamps / disconnect any trannies
turn all switches on
test each cable , continuity on the cables indicate switch lines , the rest will be loop in loop out
 
Disconnect all the cables take out fuse / mcb

Remove all lamps / disconnect any trannies
turn all switches on
test each cable , continuity on the cables indicate switch lines , the rest will be loop in loop out

But the real question do you have a tester?
 
seperate all the cables , take out all the lamps , isolate circuit, turn all switches on test for continuity on each cable , open circuit cables will be loop in loop out
 

Reply to Lighting circuit issue - please help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
597
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
453
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock