Hi there i went to a job guys kitchen light was not working no voltage at switch what so ever the circuit breaker was on the unprotected side of the distribution board i accidentally touched the com wire to the earth and a big spark happened and tripped the breaker never had that before in my life any ideas ?
must have been live. what made you think it was dead? was it a volt stick?
you mustnot have made a good connection with your probes. bang means live.
there was 100% not any voltage at that common side of the switch i jiggled the wires about inside the conduit to see if i was getting anything and still not anything just incase there was a slack connection but it banged when touched earth but honest not any voltage present it’s confused me for days
no honest was dead tried through my fluke t110 and my multi meter it baffled me
Rule #1 of not dying from electricity is to make damn sure it is dead before you work!
Multimeters are great, but have many ways of not telling you what you need to know (i.e. live or not) which is why they always suggest a dedicated voltage test and proving unit.
I have no idea of how big the spark was, but you can get a small one from discharging energy stored in capacitance. Seems a bit unlikely here though.
Also do they have PV or other local generation? It ought to go dead on the loss of mains but you never know...
yeah it was dead first thing i done when opened the switch up was test for any voltage which there wasent i don’t a voltage test between the earth wire and the metal conduit i got 168 volts then done it again nothing done it again voltage present then was none voltage it was fluctuating just confused with it all and on top of that finding the joint box within the conduits is go be a nightmare but surley has to be in an accessible place it’s a downstairs 4 in a block house
If you've got a voltage of 168V between a CPC and a steel conduit then something is very wrong.
It also suggests that maybe the live conductor was in fact dead and connected to neutral via the loads of the circuit and it was the conduit which was live and caused the bang.
the circuit breaker was on unprotected side of rcd some cow boy was in before me i really do appreciate all the comments just not opening a can of worms and would rather find the joint box and just re wire the kitchen light
Sounds like you need some help from someone with a bit more experience. If nothing has been isolated, I wouldn't recommend 'jiggling the wires about inside the conduit' to see if you're getting something...it bites, as you nearly found out.
The fault needs finding before deciding to rewire something.
To be honest, what you were doing also sounds a bit Yeehaa to me.
The problem was that the light had stopped working, so there was a fair chance of a loose connection or bad contact somewhere. You left the circuit live and started tinkering around with it, believing that the permanent live feed was dead, even though that might well have been caused by the bad connection and ever so close to making contact again. You were trusting your safety to a tiny layer of corrosion or a wire floating about in a terminal one thousandth of an inch away from being live. I think if you refer back to your procedure for safe isolation, that doesn't count!
A broken circuit is much, much safer to find with dead tests, and sometimes easier too as you don't need to keep isolating and re-energising when you want to touch anything. Continuity to the lamp? Nope. Continuity to the switch? Nope. OK, problem is upstream of the switch. Just test methodically along the circuit until you find where the continuity ends. That way, when the fault does something unexpected, it will be the tester doing the bleeping, not you.
So @The apprentice you got an intermittent reading of 168v between L and the conduit. What do you make of that? What do you think has occurred? First if the conduit/wiring has been installed properly there will be a fly lead from each connector box to earth. Normally if you test between L-E would you expect there to be a voltage reading, and if so what voltage would you expect? I am guessing that the system is T-N-CS?
ok understand i got some stuff wrong thankyou for the help i really do appreciate it
[automerge]1590409047[/automerge]
What does it matter if the lighting circuit had no RCD protection. I bet 90% of houses wired pre 2008 have no RCD protectionto domestic lighting circuits. Doesn’t make the person who wired it a cowboy.
when it’s a split rcd board? indicates it’s bn left like that for a reason
What’s wrong with the MCB for the lighting circuit being non RCD protected? Maybe if a recent installation and contrary to current regs but most older installations won’t have RCD protection ...certainly for lights.
Only if the regulations required it to be when it was installed.
Lighting and many other circuits were accepted as non rcd protected. Hence the split boards. When was the circuit installed?
Reply to lighting in the UK Electrical Forum area at ElectriciansForums.net
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...