Hey pepes.
I'm a bit new to Ryefield boards, so maybe an obvious one.
While installing the Ryefield boards in the risers to feed the flats in a tower block (40 floors), we were told to remove the PME links from within the boards.
Should there only be a link at the supply, as it is a PME system.
What difference does it make?

Thanks for any help you can give me.
 
I don’t know physically where you’ll find the N→E in a Ryefield board other than the obvious place, connected to the neutral bar.

As to what difference it makes, as an electrician you should know the theory of PME and the reasons there should only be one N→E link in a system.
 
Hey pepes.
I'm a bit new to Ryefield boards, so maybe an obvious one.
While installing the Ryefield boards in the risers to feed the flats in a tower block (40 floors), we were told to remove the PME links from within the boards.
Should there only be a link at the supply, as it is a PME system.
What difference does it make?

Thanks for any help you can give me.

As Tony stated, only the one N-E connection and that would normally be at the service head. But maybe this large tower block is supplied via it's own DNO TX into a switchboard...

BTW, how many rising mains does this 40 storey tower block have??
 
Im a bit of a Newby to this kind of thing. I'm normally a flat rat.
There is a ryefield every 3 floors to feed around 27 flats, and each swa will feed 3 ryefield boards. About 400 flats in all.
I guess this would be a PNB system. I've never been in the substation.
Obviously removing the PME link was very simple. But why? The swa comes from the main panel with a seperate bond.
 
Im a bit of a Newby to this kind of thing. I'm normally a flat rat.
There is a ryefield every 3 floors to feed around 27 flats, and each swa will feed 3 ryefield boards. About 400 flats in all.
I guess this would be a PNB system. I've never been in the substation.
Obviously removing the PME link was very simple. But why? The swa comes from the main panel with a seperate bond.

Never heard of a tower block distribution system being laid out like that. So what size are these SWA cables feeding 3 X 9 or 10 way Ryefield boards?? Got a photo of one of these completed Ryefield boards??
 
they're 185's. Cable gang put them away. Can't get any pics at the mo, not working in that area for a while. Will be going back to it after xmas.
The ryefields are 3 rows of 10 ways.
 
Per floor?

No, he stated one Ryefield per 3 floors and stated 27 flats per ryefield so i'm assuming one 10 way row for each floor...

All i know is, that definitely wouldn't be the way i'd go about providing a distribution system for a 40 floor residential tower block!!

Just think about it for a moment or two, 1 X 185mm 4 cores plus bonding cable feeding supposedly a busbar chamber that then feeds local ryefield panel and another 2 X 30 way Ryefield panels located at 3 floor intervals. At each Ryefield panel 20 smaller 16/25mm 3 core SWA to supply apartments over the next two floors, ..All sounds bloody ridiculous to me!!

Why is not each floor being utilised as the distribution point for the apartments located on that floor, rather than a distribution point that can be located 3 floors distant??


The more i think about it, the more problems i can see...
 
I’d have thought they would have gone for busbar risers with tap-offs on each floor. 81 flats on each feed is going to be pushing it.
 
I’d have thought they would have gone for busbar risers with tap-offs on each floor. 81 flats on each feed is going to be pushing it.

That would be the sensible way of doing things!! I just hope these riser cupboards have plenty of room in them!!
 
1 x 4c185mm[SUP]2[/SUP] + 81 x 3c16mm[SUP]2[/SUP] in one cubical just doesn’t bear thinking about. It would be funny to watch them sort it out. 16mm[SUP]2[/SUP] being a rough guess.

Added to which I don’t think 185mm[SUP]2[/SUP] would be up to the job.

Personally I think the OP has got things mixed up a tad.
 
Sorry for the delay, been away for a bit.
The landlords DB's are also every 3 floors, for corridor lighting and sockets, stairway lighting and what have you. These are fed by busbar trunking, Tapped off every third floor. This is because the Landlord's power requirements is not so substantial. But to supply 400 flats off of busbar trunking (that's 400x100A fuses), is going to be very expensive. Space is tight in the risers, so forget about putting multiple busbar trunking, it takes up too much room.
At each Ryefield board, there will be a maximum of 30 flats being supplied. That's 10x3c25mm cables out of the header trunking, running up the riser to the floor above, 10x3c25mm cables out of the header trunking and out through a letterbox to feed this floor, and 10x3c25mm cables from the bottom of the ryefield board and down to the floor below.
Each header trunking is over 150mm2 and over a meter long. Each Ryefield board is about 600/700mm wide and about 1000mm in height.
 
Just done a search and Eaton's range only goes up to 6300A, shneiders to only 5000A.
So we are talking about 6 or 7 busbars to feed that lot. Just isn't the space for that.
 
Sorry for the delay, been away for a bit.
The landlords DB's are also every 3 floors, for corridor lighting and sockets, stairway lighting and what have you. These are fed by busbar trunking, Tapped off every third floor. This is because the Landlord's power requirements is not so substantial. But to supply 400 flats off of busbar trunking (that's 400x100A fuses), is going to be very expensive. Space is tight in the risers, so forget about putting multiple busbar trunking, it takes up too much room.
At each Ryefield board, there will be a maximum of 30 flats being supplied. That's 10x3c25mm cables out of the header trunking, running up the riser to the floor above, 10x3c25mm cables out of the header trunking and out through a letterbox to feed this floor, and 10x3c25mm cables from the bottom of the ryefield board and down to the floor below.
Each header trunking is over 150mm2 and over a meter long. Each Ryefield board is about 600/700mm wide and about 1000mm in height.

Just done a search and Eaton's range only goes up to 6300A, shneiders to only 5000A.
So we are talking about 6 or 7 busbars to feed that lot. Just isn't the space for that.

You haven’t a clue what you’re talking about have you? What is your role in this project?

No one in their right mind would install a single riser. There’s no way am I going in to X linked risers on here.
One failure = total blackout = 400 unhappy tenants = landlord’s rep hanging by his ankles out of a top floor window.
Added to which, cables traversing three floors isn’t going to go down well with the fire authorities.

Just to add to your misery, have a look for the DNO’s diversity figures for residential dwellings. (A hint, you’ll not find it in the OSG or BGB)

Stick to wiring the corridor lights off the landlord’s boards and making the tea for the guys that do know what they’re doing.
 
Tony.
Not only are you a grumpy git, as you state in your profile. But what you failed to mention is the fact that your head is stuck so far up your own arse that you cant even read.
You repeatedly get it all wrong. Even in this thread, no matter how clear it is made, you keep getting it wrong and another member who was reading the very same posts has had to clear it up for you. And by the way, was far more help than you in just one of his posts than you ever have been. I got a reply from you on a previous post and you got it all wrong that time too. Fortunately, there are some helpful sparks on here that can actually read.
Read the posts man.
I didn't design this. I am an electrical installer who is working by the drawings.
As stated, there is a landlords riser and a residential riser. Many other risers too.
But only one riser that feeds the flats.
Yes, this is allowed. I know this because Ive seen it many times before. I don't know where you get the idea that cables going though 3 floors is wrong. The only cable that traverses 3 floors is the supply cable. Which by the way, comes all the way from the basement (a bit more than 3 floors).
The SWA from the ryefields to the meters goes a maximum of 1 floor, either up or down.
All risers are fire protected.
Please, keep your divine wisdom for yourself and your family. Because all it is doing here is going to waste.
 
Sorry for the delay, been away for a bit.
The landlords DB's are also every 3 floors, for corridor lighting and sockets, stairway lighting and what have you. These are fed by busbar trunking, Tapped off every third floor. This is because the Landlord's power requirements is not so substantial. But to supply 400 flats off of busbar trunking (that's 400x100A fuses), is going to be very expensive. Space is tight in the risers, so forget about putting multiple busbar trunking, it takes up too much room.
At each Ryefield board, there will be a maximum of 30 flats being supplied. That's 10x3c25mm cables out of the header trunking, running up the riser to the floor above, 10x3c25mm cables out of the header trunking and out through a letterbox to feed this floor, and 10x3c25mm cables from the bottom of the ryefield board and down to the floor below.
Each header trunking is over 150mm2 and over a meter long. Each Ryefield board is about 600/700mm wide and about 1000mm in height.

Just done a search and Eaton's range only goes up to 6300A, shneiders to only 5000A.
So we are talking about 6 or 7 busbars to feed that lot. Just isn't the space for that.

YOU read YOUR posts #1 #4 #7 and then tell me what I’ve misunderstood. All we can do is go on the information provided.

Not until #14 do you say there’s multiple risers. Then #15 you comment on the size of the riser.

I can assure you the loading does not = 400x100A which is why I said to look for the DNO’s diversity figures.
 

Reply to Location of PME Links in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
559
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
539
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Replies
4
Views
1K
hi there.. bit advice please..im installing 24 way ryefield board..im bit confused for neutral bar ..neutral bar its linked to body of ryefield...
Replies
2
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock