bororich

hi guys...
i have been testing lately and have found my megger 1553 has been giving me higher r1+r2 results than the Zs results... i use the same leads, always use good batteries and have it calibrated? is the machine at fault? has anyone ever had similar experiances? im aware that there maybe parralell earths aswell but it is happening too often to be that...

please help!
 
Check you not getting confused by parallel earth path like metal conduit, armour, trunking or metal building structure if linked to the back of a metal box?
 
yeah i have checked this there is no parallel earth path on this circuit i did today.... twin and earth cable into a plasterboard box.. it has really confused me? mates at work are stumped too!!
 
Its probably just a poor connection only showing up when you do the ohms test off the battery in your meter, as the mains voltage 200 plus volts more than the battery test and is not showing this problem.
The cables are all probably in and screwed bit one probably needs tweaking tighter.
 
i will replace the leads and get back to you.. they seem fine visually but i will swap them for another set. thank you for the advice
 
Hi

You have stated you have changed the batteries, so after checking the test leads it is possible the unit may have a fault.
Have you noticed any difference in readings between the mains test lead and the 3 individual leads?

Regards

Megger TSG
 
mine does the same on no trip but ok on high i think it uses the neutral on no trip as the other day i had a skt with no earth on high it came up 55v well no response when i put it on no trip it took a reading
 
are you using fused leads? sometimes they unscrew a little and have you checked the obvious nulling the leads?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
megger strange test readings... help!!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
bororich,
Last reply from
jjjinx,
Replies
10
Views
2,756

Advert