mkemp590

DIY
Reaction score
0
Hey all,
I'm running a few outlets to my basement from the main panel on the first floor. Since it is a garage, sealed 3/4" pvc conduit runs through the concrete into the basement. This connects to a metal junction box and 3/4 emt, with metal junction and outlet boxes the rest of the way. There are two 20 amp circuits and one 15 amp circuit for the lights. I know that I can use the emt itself as the ground path as long as it is connected to the main panel. My question is: Would it be code compliant to run one ground wire from the main panel, through the pvc, to the first metal junction box, and then ground all of my outlets to their outlet boxes further down the line?
Thanks for the input!
-Matt
 
Run a ground wire throughout AND bond to all metal boxes with ground screw or at least to the outlet itself. Using EMT or any conduit as a ground or bond has been against the NEC (US code book), for any new installation, a good long while. The ONLY exceptions are if you don't touch it, or install a GFCI & bond to the box.
The path to ground is the most important circuit in an electrical system. I would call a local electrician for advice as to any local codes in your city/state that I maybe unaware of.

Good luck
 
Last edited:
Hey all,
I'm running a few outlets to my basement from the main panel on the first floor. Since it is a garage, sealed 3/4" pvc conduit runs through the concrete into the basement. This connects to a metal junction box and 3/4 emt, with metal junction and outlet boxes the rest of the way. There are two 20 amp circuits and one 15 amp circuit for the lights. I know that I can use the emt itself as the ground path as long as it is connected to the main panel. My question is: Would it be code compliant to run one ground wire from the main panel, through the pvc, to the first metal junction box, and then ground all of my outlets to their outlet boxes further down the line?
Thanks for the input!
-Matt
Matt PVC or not you are required to pull 1ground wire per raceway sized to coincide with the largest conductor
 

Reply to Mixed conduit grounding question in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock