cdisney

Hi all
I am in the middle of wiring my extension and just after some advice regarding the appliances.

I am thinking of running a radial to a double back box for grid switches for four appliances (freezer, washing machine, tumble dryer and fridge) and then having a sepearate kitchen ring.
Is this best option or can I have the appliances on the ring main too?

Thanks
 
It'll be tight in that back box....
 
If you had the appliances on the grid switch that was fed by the ring final circuit then you would have make sure the grid switch was bang in the middle of the ring..I personally think having the grid on a ring final is bad design. What size radial was you thinking of running and what would the installation method be?
 
  • Agree
Reactions: Dave OCD
It will be run under the floorboards and then capped to the back box and then 2.5mm to a single socket for each appliance, protected by 20A mcb on a splitter board
 
Well technically you can only put 4mm^2 on a 32A MCB if it's installed ref method C for it's whole length. Are there any other derating factors?
 
No insulation etc and it is only around 7/8 Mtr run.
Can I use 2.5mm as struggling to get 4mm for tomorrow
 
  • Optimistic
Reactions: kingeri
I was about to say the same...if you go on the averages of 500W freezer, 200W fridge, 2500W tumble dryer and 2000W washing machine when heating.....Thats about 22A. I don't like grid switches and would just install the appliance sockets in an adjacent cupboard. If you do want a grid switch then I would look at taking a couple of feeds to it.
 
  • Agree
Reactions: kingeri
No because you could overload a 2.5 with those appliances, frankly you seem to be guessing here and for your own safety you should get an electrician in.
 
  • Agree
Reactions: kingeri
You really need an electrician. If you use 2.5 then you will have to use a 20A breaker. That could well be overloaded with those appliances. Also it isn't a great idea to have fridge and freezer on with other stuff....given the opportunity these could go on dedicated circuits.
 
He has been on the forum since 2012 and it would help if he filled his profile in,
 
He has been on the forum since 2012 and it would help if he filled his profile in,
His missus must be fed up waiting to get those appliances up and running by now eh. :D
 
Two separate circuits seems a lot of extra work just to have extra isolation points. Going to run the appliances on a dedicated 32A ring and then also have a kitchen ring.
Thanks for the help kingeri
 
Two separate circuits seems a lot of extra work just to have extra isolation points. Going to run the appliances on a dedicated 32A ring and then also have a kitchen ring.
Thanks for the help kingeri
eh...it's the same amount of cables 2xrfc is 4 cables 1xrfc and 2xradials is 4 cables.
 
  • Like
Reactions: Dave OCD
That is correct but I don’t have any 4mm and not likely to get any tomorrow and have to be done by end of play tomorrow. Also less due to cable to each appliance from switch.
 
Due to the position of the separate integrated fridge and freezer I am going to have switched fuse spurs on other side of the wall and a single socket on load side. Looking at regs there is nothing to say there is anything wrong with this.
Does anyone have thoughts on this?
 
That is correct but I don’t have any 4mm and not likely to get any tomorrow and have to be done by end of play tomorrow. Also less due to cable to each appliance from switch.
Screwfix sell it and open on Sundays if you want 4mm.
 
Due to the position of the separate integrated fridge and freezer I am going to have switched fuse spurs on other side of the wall and a single socket on load side. Looking at regs there is nothing to say there is anything wrong with this.
Does anyone have thoughts on this?
sounds carp to me.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New extension Kitchen appliances
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
cdisney,
Last reply from
HandySparks,
Replies
26
Views
2,166

Advert