Unfortunately if you do not have a compliant system it is difficult to complete the paperwork, however one could say that the CU replacement was successful but the circuit in question is faulty and has been disconnected. (pending further investigation!)
With a resistance of a 2.5mm cable being 0.008ohm/m you must have a link fault within 0.5m of the CU as anything above that would likely show as 0.01ohm and not as zero on the meter (depending on the meter resolution). Assuming your batteries are up to spec. in the meter.
Best way to test I would say is to disconnect all the RFC wiring from the CU keep all the ends separate join your meter with a long lead to one of the, say neutral, cables and go round each socket with the meter and test the resistance of that one wire (using a socket adapter); if the resistance is zero all the way round, then there is a problem with your meter, if the resistance increases up to the middle and then decreases as you reach the other end of the ring then the ring is linked close to the meter, if the resistance increases each time you move further away then try starting at the other end of the (in this case neutral) cable if again the resistance increases steadily... Ah bit stuck but you could use the largest value as close to n-n reading (no do not do that, that is wrong) but ring should be OK. Similarly with the line conductor.
Good luck with the assessment, do talk to the assessor and they should be understanding, they normally do want you to pass even if only to get your money!