Hi all, just wondered if one of the members could shed a light on my result of a Ze test. I have just changed my ccu in my ex council house in order to add 2 new circuits(mains powered smoke and heat detectors and also a mains feed for my alarm). The house was rewired about six years ago so the cables and fittings are in good condition and the correct sizes, but in the old colours. The ccu that i changed feeds all circuits in the house except for the electric storage heaters that are on their own ccu and operated by an economy 7 radio time switch. I have tested every circuit to BS7671 2008 (both dead tests and live tests). Everything seams ok and has been recorded on the apropriate cert, except for the Ze test. The 16mm earth to new ccu, the earth to the heaters ccu and the 10mm earth bonding to water(no gas feed in house) are all connected to the earth terminal enclosed in the TNCS enclosure which houses the 100amp cut out fuse. fortunatly ther is no seal on the cut out so i was able to remove fuse and gain access to the earth terminal to remove the other earth to do the test. I isolated the heater ccu before dissconnecting its earth. I then dissconected the earth from the new ccu and connected my megger1552 to the correct point and tested the Ze. The result i got was very low and caused some disbelief on my part( 0.07 ohms) as i was expecting around 0.34ohms. i did this test serveral time with the same results. The megger did indicate that ther was some Interference some where, but all circuits were isolated apart from the radio time switch so not sure if this result is valid. This has to be acuratly measured as this job is to be used for 1 of my assessments for self cirtification. Also the meter cables are the old colours is it ok as on is off meter and one off cut out (seald Meter). cheers
 
Hi there.

Are you saying you disconnected all other earthing conductors from the MET and left just the earth under test there by eliminating all parallel paths??

It could be that you are very close to a sub-station transformer and with it being a TN-C-S system the earth is very low.

What reading did you have for PFC?? was this high?? If it is the case I would expect a reading of around 3285A.
 
.07 is fine its quite common in my area to be low because you are never far from the transformer
the job in the photos in the show us your installs section i posted has ze of .10 and they were recorded by the dno and were happy
as lenny said just watch your ka reading
 
Thanks, yes i dissconnected all other earthing conductors from the MET. My PFC reading was 3.3Ka. As for the meter tails which are 25mm black and red do i need to change these as 1 is from a henley block which i could change and 1 is from the meter which has a seal on ang therefore not permissable touch. Thanks again, knowledge is power.
 
it the tails are 25mm dont worry about the colour. If you want to be correct wrap some tape round them to mark them. you dont have to change them. besides what means you got to isolate the main incommer to D.B ?
 
Cheers. The cut out has not been resealed since the house was rewired 6 years ago by some contractor working for the coucil. see attached pic of ccu,s.
 
HI everyone Just Ihad exam 2391, the question was many special location in domestic installtion?
My answer, was nine special location,is that right or wrong
 

Reply to Odd Ze test result. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
677
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock