Discuss Part 1 : Skilled Tradesman?? in the UK Electrical Forum area at ElectriciansForums.net

S

SparkyDips

ok guys here's the story........building lost power due to break in main supply cable, electricity board decided its easier to move headers (3 phase and single phase) to new location by cutting and re-routing main supply cables.

joint completed

IMG_2186_zps2cb17140.jpg


Now.....

all that is needed is 4 new supply cables to be run around the premises (seperate buildings) to each CCU location, i have refused to have any involvement with this work as its a big c###up from the start.

temporary supply is provided by 10mm T&E run all over the place.....

IMG_2130_zps8c607aa0.jpg


so said "tradesman" has stepped up saying he has worked out the volt drops to each CCU and 3 core 35mm SWA is needed for 3 locations and 70mm SWA for one..........or in this case 2 35mm's run in parallel!!!

so he runs all cables to CCU locations and TRIES to terminate 4 35mm SWA's into.......

IMG_2183_zpsaf2b7834.jpg


nice busbar!!!

and a single 35mm into.....

IMG_2184_zps96b2fe65.jpg


having now realised this isnt 'big enough' he orders a metal 3 phase board, NO BREAKERS, and well, heres the pics..........

IMG_2209_zps0f724bbb.jpg


IMG_2208_zpse6c6bc97.jpg


IMG_2207_zps5198ca23.jpg


IMG_2210_zpseb894dcb.jpg


IMG_2212_zps64bc0ace.jpg


IMG_2211_zpscf27ab03.jpg


sponsored by theWildWest.com!!!!!
 
I can't begin to imagine what's going on in that db. Like how he paralleled his 2 35mm line conductors into a single mcb.

What's the current status of this job ? Has this guy been chained up in the boiler room for his own safety ?
 
ok guys here's the story........building lost power due to break in main supply cable, electricity board decided its easier to move headers (3 phase and single phase) to new location by cutting and re-routing main supply cables.

joint completed

IMG_2186_zps2cb17140.jpg


Now.....

all that is needed is 4 new supply cables to be run around the premises (seperate buildings) to each CCU location, i have refused to have any involvement with this work as its a big c###up from the start.

temporary supply is provided by 10mm T&E run all over the place.....

IMG_2130_zps8c607aa0.jpg


so said "tradesman" has stepped up saying he has worked out the volt drops to each CCU and 3 core 35mm SWA is needed for 3 locations and 70mm SWA for one..........or in this case 2 35mm's run in parallel!!!

so he runs all cables to CCU locations and TRIES to terminate 4 35mm SWA's into.......

IMG_2183_zpsaf2b7834.jpg


nice busbar!!!

and a single 35mm into.....

IMG_2184_zps96b2fe65.jpg


having now realised this isnt 'big enough' he orders a metal 3 phase board, NO BREAKERS, and well, heres the pics..........

IMG_2209_zps0f724bbb.jpg


IMG_2208_zpse6c6bc97.jpg


IMG_2207_zps5198ca23.jpg


IMG_2210_zpseb894dcb.jpg


IMG_2212_zps64bc0ace.jpg


IMG_2211_zpscf27ab03.jpg


sponsored by theWildWest.com!!!!!
eh?...
lol...lol...lol...
 

Reply to Part 1 : Skilled Tradesman?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
478
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
293
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock