Apologies if this is the wrong sub-forum for this. I work for a large UK university and we've had a few incidences at work now of multi-way trailing sockets with bad earths on one or more of the sockets. Currently they are PAT tested by an external contractor who (I believe) just tests earth continuity at the socket most distant from the flex. This is clearly not picking up the units with just one faulty earth - e.g. the socket contacts have separated from the bus bar.
As we use an external company for PAT testing who charge a fee per test, if we were to test each socket individually the cost would be astronomical.
Is there any industry best-practice guidance for this scenario? I've ordered a copy of the IET code of practice from our library but it will take a long time to arrive.
It has been suggested that we use a 3-light socket tester to verify the earth in each socket. This doesn't test the earth continuity at 25A though like a 'proper' PAT test which is an issue but it is certainly better than nothing. I see Martindale do one which shows the earth impedance which I think would be better still:
Buy Mains Socket Testers Martindale EZ150 Mains Socket Tester 13A 230V ac CAT II 300 V, Model EZ150 RS Calibration Martindale EZ150 online from RS for next day delivery.
What are people's thoughts on this?
Cheers!
Apologies if this is the wrong sub-forum for this. I work for a large UK university and we've had a few incidences at work now of multi-way trailing sockets with bad earths on one or more of the sockets. Currently they are PAT tested by an external contractor who (I believe) just tests earth continuity at the socket most distant from the flex. This is clearly not picking up the units with just one faulty earth - e.g. the socket contacts have separated from the bus bar.
As we use an external company for PAT testing who charge a fee per test, if we were to test each socket individually the cost would be astronomical.
Is there any industry best-practice guidance for this scenario? I've ordered a copy of the IET code of practice from our library but it will take a long time to arrive.
It has been suggested that we use a 3-light socket tester to verify the earth in each socket. This doesn't test the earth continuity at 25A though like a 'proper' PAT test which is an issue but it is certainly better than nothing. I see Martindale do one which shows the earth impedance which I think would be better still:
Buy Mains Socket Testers Martindale EZ150 Mains Socket Tester 13A 230V ac CAT II 300 V, Model EZ150 RS Calibration Martindale EZ150 online from RS for next day delivery.
What are people's thoughts on this?