Apologies if this is the wrong sub-forum for this. I work for a large UK university and we've had a few incidences at work now of multi-way trailing sockets with bad earths on one or more of the sockets. Currently they are PAT tested by an external contractor who (I believe) just tests earth continuity at the socket most distant from the flex. This is clearly not picking up the units with just one faulty earth - e.g. the socket contacts have separated from the bus bar.

As we use an external company for PAT testing who charge a fee per test, if we were to test each socket individually the cost would be astronomical.

Is there any industry best-practice guidance for this scenario? I've ordered a copy of the IET code of practice from our library but it will take a long time to arrive.

It has been suggested that we use a 3-light socket tester to verify the earth in each socket. This doesn't test the earth continuity at 25A though like a 'proper' PAT test which is an issue but it is certainly better than nothing. I see Martindale do one which shows the earth impedance which I think would be better still:

Buy Mains Socket Testers Martindale EZ150 Mains Socket Tester 13A 230V ac CAT II 300 V, Model EZ150 RS Calibration Martindale EZ150 online from RS for next day delivery.

What are people's thoughts on this?


Cheers!
 
The cheapest route would probably be to ensure that your specification requires all sockets on multi gang extension leads to be tested by the PAT company. If you slip this requirement in next time you tender the contract, it will probably cost you very little more.

In the meantime, I think you could take this up with your existing contractor. You are paying them to verify the safety and integrety of these leads and the tests that they are doing are obviously falling short of achieving this.

Out of interest, how many failed units have you discovered so far?

If you work for Estates and you're not already a member, consider joining the Association of University Engineers: Home - aue
 
All individual items should be tested anyway,thats how you find the faulty ones .

Google the Seaward site they have all the information you need on this subject .


Sorry , you are to quick for me lol.
 
Thanks All,

After a bit of faffing about I've found this on the Seaward site:

http://www.seaward.co.uk/downloads/015-create-a-test-sequence-for-a-multi-way-lead.pdf

Which basically allows you to modify the test to include an unlimited number of earth continuity tests so you can test each socket separately but all under one overall test. I'll recommend that we do this and leave it to the bean-counters to negotiate this with the external PAT testers.

Cheers!

Also, as requested: last year we had three items which I'm aware of:

One 4-way strip with a cracked spot weld on the earth bus bar. That was in my workshop, noticed it when I was getting 200v p-p on my oscilloscope when touching the probe :)

also two large (around 12 way I think) strips from rack units that are wired internally with singles and bootlace ferrules had some sockets with dodgy earths.
 
From memory the Code of Practice does point out that all socket outlets would need to be separately tested for earth continuity.
 
This has been part of my PAT specification since the year dot. I agree it is an important test and many items - especially budget 4-ways and extension reels - show up with the contacts bent, slack, or detached entirely. The cause often seems to be the plastic moulding giving way, allowing the contact itself to get out of position and scrunched up by the next plug to be inserted.

I would avoid the socket-tester scenario as the go/no-go of a neon is inadequate to check the quality of contact, plus very little extra time is needed to do it on the PAT machine. Since I first started using automatic testers I've added programs for 4 and 6-outlet plastic distros (with 4 or 6 tests) and also for metal ones (with 5 or 7 tests to include the case). No-one here would think of not testing all the outlets, and the same for multiway IEC cables / blocks, UPS IEC outlets etc.
 

Reply to PAT testing of multi way socket strips. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
690
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
784
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
745
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock