Discuss pir and main bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
cagedanimal2010
Morning guy, cant seem to find the reg that states a bonding conductor cant be cut???
A nudge in the right direction would be greatly appreciated! Thanks guys!!
One conductor eye crimped to water, then another conductor taken from that point(water connection) eye crimped also.
so guys, i have always been under the impression that you can bond water and gas with one conductor as long as you don't cut it? is this right or wrong?
thanks in advanced!
danny
correct. ot's so that if, say, the bonding cable goes to the gas then the water, if the connection is removed from the gas, the bonding to the water is still intact. whereas if it were 2 cables, joined at the gas bonding clamp, both would be lost.
thanks in advanced!
danny
Perfectly correct, you can in theory 'loop' from gas to oil to water etc. with an unbroken cable.
There is no regulation but Guidance Note 8 and probably Guidance Note 1 explain this procedure along with the 'no broken conductor' proviso.
Code 4 for me.
Reply to pir and main bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...